    Hmm

    I have a Heil furnace......when the target temperature is hit the furnace blower continues to run and does not shut off. I can even set the target temperature below the actual temperature and it still runs.
    What is going on with this thing?

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    16,438
    Make sure that the fan switch at the tstat is in the auto position. Other then that, you may have a bad relay, circuit board, or comb. fan/limit control and will need to patronize your local heating contractor.
    "If anybody can draw on the power, where do we put the meter?" - JP Morgan before pulling Tesla funding

  3. #3
    Join Date
    Sep 2002
    Posts
    495
    Doesnt shut off soon enough for YOU? or never shuts off?
    If I know I'm going Crazy,I must not be Insane

  4. #4
    Join Date
    Feb 2005
    Posts
    2

    Heil Furnace

    The blower will stay on always.......will not shut off unless I turn off power.
    I have checked the position of fan....it is in the auto position not the on position.

  5. #5
    Than you need to call for service.

  6. #6
    gasman Guest

    Smile

    either the relay switch stuck closed or the fan switch is stuck on fan/limit control.