I have a Heil furnace......when the target temperature is hit the furnace blower continues to run and does not shut off. I can even set the target temperature below the actual temperature and it still runs.
What is going on with this thing?
-
02-25-2005, 05:39 PM #2
Make sure that the fan switch at the tstat is in the auto position. Other then that, you may have a bad relay, circuit board, or comb. fan/limit control and will need to patronize your local heating contractor.
"If anybody can draw on the power, where do we put the meter?" - JP Morgan before pulling Tesla funding
-
02-25-2005, 05:51 PM #3
Professional Member
- Join Date
- Sep 2002
- Posts
- 495
Doesnt shut off soon enough for YOU? or never shuts off?
If I know I'm going Crazy,I must not be Insane
-
02-26-2005, 01:20 PM #4
Regular Guest
- Join Date
- Feb 2005
- Posts
- 2
Heil Furnace
The blower will stay on always.......will not shut off unless I turn off power.
I have checked the position of fan....it is in the auto position not the on position.
-
02-26-2005, 02:19 PM #5
Grumpy Old Man
- Join Date
- Apr 2003
- Posts
- 6,383
Than you need to call for service.
-
02-26-2005, 03:02 PM #6gasman Guest
either the relay switch stuck closed or the fan switch is stuck on fan/limit control.