    I have a Heil furnace......when the target temperature is hit the furnace blower continues to run and does not shut off. I can even set the target temperature below the actual temperature and it still runs.
    What is going on with this thing?

  2. #2
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    22,170
    Post Likes
    Make sure that the fan switch at the tstat is in the auto position. Other then that, you may have a bad relay, circuit board, or comb. fan/limit control and will need to patronize your local heating contractor.
    “Socialism is a philosophy of failure, the creed of ignorance, and the gospel of envy, its inherent virtue is the equal sharing of misery.”

  3. #3
    Join Date
    Sep 2002
    Posts
    496
    Post Likes
    Doesnt shut off soon enough for YOU? or never shuts off?
    If I know I'm going Crazy,I must not be Insane

  4. #4
    Join Date
    Feb 2005
    Posts
    2
    Post Likes
    Thread Starter

    Heil Furnace

    The blower will stay on always.......will not shut off unless I turn off power.
    I have checked the position of fan....it is in the auto position not the on position.

  5. #5
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Than you need to call for service.

  6. #6
    gasman Guest

    Smile

    either the relay switch stuck closed or the fan switch is stuck on fan/limit control.