    Apr 2006
    checking a heat exchanger
    Am I correct in thinking that if I used my combustion analyzer and put it the supply air stream, that a high CO reading would indicate a bad heat exchanger? Would anything above 0 ppm mean a bad heat exchanger?
    Dec 2010
    The Colony, TX.
    absolutely correct there should be no co detected in the supply air and the only thing i have ever seen that would cause that would be a cracked heat exchanger.
    Dec 2009
    Southern US
    Well................
    When the unit first fires CO2 would be present but when the blower starts it would usually force supply air back into the exchanger. Thats why the rollout switch trips.
    I'm good at making things cold...You can ask my first two wives!
    Apr 2005
    where the beer flows like wine
    I dont think with a draft inducer any CO would leak into the supply duct at all regardless, even with a gravity system is kind rare to have CO leaking from the HX into the conditioned air, just check the combustion byproducts for o2 increase after the blower kicks in.
    Dec 2009
    Southern US
    Quote Originally Posted by hvacpope View Post
    You know I had never really looked at it that way, I think your right!
    Jun 2009
    Bakersfield, Ca
    Couldn't CO be released from oil burning off of a fresh h/x? Dust?
    Aug 2010
    Chicago, IL.
    If this is true then we're replacing units with a cracked HX because of what? High combustion chamber temperatures only? I taught CO leaking into the supply stream was a major concern also?
    Learn to live, so that you may live to learn.
    Dec 2010
    On a Peninsula in NE NC
    if the gas x changer is bad it prolly will be opened up on the top, or supply side creating a negative at that spot, drawing out combustion air, but if on bottom it will be pressurizing the chamber causing roll out. Yes No?
    May 2008
    Central Pennsylvania
    I've never tried using a combustion analyzer on an RTU, but I would think if the HX was cracked you would probably pick up CO in the supply side. Yes you have a draft inducer but the supply fan moves a lot more air.
    Dec 2010
    Quote Originally Posted by chillerguy81 View Post
    you have never used one to set up valves and dampers to see how it was burning from stack measurement's?
    Apr 2005
    very simple rule, high pressure moves to low pressure, a cracked HX would mess the combustion efficiency big time but very rarely would do more than that, where is captain CO when you need him?
    Dec 2009
    Southern US
    Interesting!
    I think the next PM's I do on one of our older buildings where there is a good chance of heat exchanger problems, I'll try to take one of our analyzers and run some checks.
    Southeastern Pa
    That was my opinion until last week, when I had a call for a "gas smell" at one of the few remaining video stores outside Philly. The manager said the smell was coming from the register in the entrance alcove.
    On the roof, there was an old york 150 with a perforated hx. Inducer ran great, but combustion byproducts WERE finding their way into the supply air.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules: