what winding is open when compressor overheats, c-r,r-s,or s-c?
-
02-26-2005, 02:20 AM #2
Regular Guest
- Join Date
- Jan 2005
- Posts
- 175
Never really paid attention to that, if compressor was hot to the touch and windings open, I cool it down with water and wash condenser out for good measure, test the capacitor with my Supco tester, test run unit after windings close and figure out my problem. Usually it is a bad run capacitor or bad condenser fan motor causing compressor to overheat (assuming unit has gas in it and no hi pressure switch).
-
02-26-2005, 02:29 AM #3
Professional Member
- Join Date
- Feb 2003
- Posts
- 538
It's the common
-
02-26-2005, 02:31 AM #4
Regular Guest
- Join Date
- Feb 2005
- Posts
- 15
thank you for the infoOriginally posted by mech890
It's the common
-
02-26-2005, 09:20 AM #5
Professional Member
- Join Date
- Nov 2004
- Posts
- 2,923
Is it a trick question? There is no "common winding."Originally posted by jgb123
what winding is open when compressor overheats, c-r,r-s,or s-c?
If you get open between C-S,or C-R but ohms between R-S then you might have open overload.If open between R-S,then it is open winding,burned compessor.
-
02-26-2005, 09:23 AM #6
Regular Guest
- Join Date
- Jun 2004
- Location
- Maryland's Eastern Shore
- Posts
- 892
You'll be open between C-R and C-S...
-
02-26-2005, 10:44 AM #7
Regular Guest
- Join Date
- Feb 2005
- Posts
- 15
Originally posted by jacob perkins
Is it a trick question? There is no "common winding."Originally posted by jgb123
what winding is open when compressor overheats, c-r,r-s,or s-c?
If you get open between C-S,or C-R but ohms between R-S then you might have open overload.If open between R-S,then it is open winding,burned compessor.
thats what i thought, thanks for the info