Page 1 of 2 12 LastLast
Results 1 to 13 of 18
  1. #1
    Join Date
    Feb 2005
    Posts
    9
    Post Likes
    I would like a recommendation from the experts. I have a 10+ year old 3000 sq ft. New England house with a warm air furnace. Have seperate trunks for upstairs and downstairs, seperate oil fired HWH. Currently uses a 5 ton outdoor unit. Want to upgrade to hydro air using two air handlers and condensers, boiler with indirect HWH for domestic HW. My main question is should I pay the additional money for variable speed air handlers? I plan on using 12 seer single speed 3 ton (adding basement cooling) outdoor units due to the relativly short cooling season, but like the benefits of variable speed handlers (quiet, low speed and ramping speed heating). Two contrators are trying to talk me out of spending the money on variable speed units. The other question I have is do I need humidity control thermostats, or is there a significant benefit for those in New England?

  2. #2
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    Post Likes
    Have you had a load calculation done? If not this would be the starting point.
    What boiler are you planning on using? An oil fired hot water heater (ofwh) would be 80% efiecient and may be able to supply all your needs for a considerable savings of initial investment.
    After the load calc you may find you need the 5 ton unit for the upstairs alone.
    Variable speed motors are typically used to get extra effiency out of gas furnaces, seems a little overboard to me, a good system should be quiet anyway. You could have the system set up so the air handlers were 2 stage via blower speed in heat which would give quieter operation during much of the heat operation.

  3. #3
    Join Date
    Feb 2005
    Posts
    9
    Post Likes
    Thread Starter

    New England Hydro Air

    Plan on using either Burnham V8 or Weil Mclain Gold series boiler(depending on contractor I choose)with 50 gal indirect HW tank. One HW coil on each air handler.

  4. #4
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    Post Likes
    Again

    Originally posted by hvac-tech-lane
    Have you had a load calculation done? If not this would be the starting point.
    Burnham V8 rated from 82.1% to 86.3% what would 2.1to 6.3%of your annual heating bill be? what would be the pay back point in years, with your proposed new system you will need to run the boiler year round for domestic hot water.

    you may want to check out:
    http://www.tesmar.com/html/water_hea...the_codes.html

    Hydro heat systems are designed for use with hot water heaters and will need modification to use with a boiler system. The circulator pump will need to be removed and a zone valve utilized for proper configuration.

    Im curious is cost no object?

  5. #5
    Join Date
    Feb 2005
    Posts
    9
    Post Likes
    Thread Starter
    hvac-tech-lane, thanks for your input but I don't plan on using a HW heater as a solution to my needs. Boiler is my choice. Cost is always a consideration but the configuration that I posted in my first post is the system I'm going with. I would still like responses to my original question, thanks.

  6. #6
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    Post Likes
    As to VSAH No. As to humidity defer to local experts. And back to my original question, LOAD CALC ?

    [Edited by hvac-tech-lane on 02-19-2005 at 02:48 PM]

  7. #7
    Join Date
    Feb 2003
    Posts
    1,996
    Post Likes
    WIth an oil fired boiler, you can't modulate the burner, so why bother with the added expense of VS? I would get a multi-speed AH that would allow you to lower the fan speed durring the heat season. Get an outdoor reset control like a tekmar to run the boiler up to 180 for the indirect and vary the water temp from 140-180 on the AH's as the outdoor temp changes. A humidifier will work better on a slower fan speed so you distribute more moisture with longer fan runs.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,848
    Post Likes
    A VS blower will let you set your cfm for heat, and cfm for cooling independant of each other, and with a humidistat it will help to control humidity in your house during the cooling season.
    The ramp up will help to prevent a blast of cold air in heating, and outdoor reset will save on your fuel bill.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Aug 2004
    Location
    Springfield, Oregon
    Posts
    12
    Post Likes
    check out the Energy Saving Products website. high velocity heating and cooling with hot water coils. they also have the JH series low velocity fan coils to adapt to your exisiting duct system.

  10. #10
    Join Date
    Jun 2003
    Location
    Jacksonville, FL.
    Posts
    4,310
    Post Likes

    <long sigh>....

    And another good question would be: Why settle for a 12SEER? Go 13 & you're ready for 2006! And, besides, there's absolutely nothing wrong with wanting a VS air handler; they're the wave of the future, & one day you will no longer be able to get multi-speed air handlers. Go for broke, dude! Do what makes ya happy & don't let any contractor tell you what you want.

  11. #11
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    I wouldn't do the VS air handler if it were my house. No need to complicate the elaborate system hydro-air brings already. VS A/H are too much money anyways. Have the contractors set up the fan speeds accordingly, as they come thru on medium for heat, and high speed for cooling. Some less expensive models are set on high speed for both. A/H controls are available that will run the heat on low speed, and the A/C on medium or high. You set the speeds to fit your installation. I run nearly all heat settings on low speed, makes for more comfort, less cycling, less noise.




  12. #12
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    Almost forgot to add........do the Weil McLain Gold boiler with the Carlin Elite burner. Best USA made oil boiler combination in my opinion. I do lots of service work and this combination is by far the cleanest running combination I see, day in, day out.


  13. #13
    Join Date
    Feb 2005
    Posts
    9
    Post Likes
    Thread Starter
    What is the difference between the Carlin Elite and EZ burners?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.