    question, (still learning) if max is 60 and MCA is 38, can you not multiply 38 * 125% = 47.5 and go with a 50 amp breaker if such is available (i don't think they are)

  2. #22
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    Originally posted by phosgene
    question, (still learning) if max is 60 and MCA is 38, can you not multiply 38 * 125% = 47.5 and go with a 50 amp breaker if such is available (i don't think they are)
    You can use a 40 50 or 60 Amp breaker, whatever holds without tripping. Your wiring just has to be rated for at least 38 amps. Your wire needs to be at least #8 copper.

    Fas Eddy; If the load calc says 4.6 tons you put in a 4 ton unless the old 4 ton compressor has lost capacity and then you would put in the 5 ton?