    Post Likes

    Angry

    Having problem with air flow & humidity. I live in a split level rancher. Heater is in the attic .there is a 10 degree difference from lower floor to upper floor .starting at the lower floor 65/70/75. Humidifier can not keep up. There is a noticeable difference in air flow, upper floor to lower with the lower floor having the least.

  2. #2
    Join Date
    Dec 2004
    Posts
    201
    Post Likes
    sounds like a poor setup,,are you new to the house

  3. #3
    Join Date
    Feb 2005
    Posts
    5
    Post Likes
    Thread Starter
    not new to the house. We just had a contractor install it.

  4. #4
    Join Date
    Dec 2004
    Posts
    201
    Post Likes
    are you saying there is one airhandler in the attic supplying 3 floors

  5. #5
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    How long of a cycle does the furnace run ?

  6. #6
    Join Date
    Feb 2005
    Posts
    5
    Post Likes
    Thread Starter
    its a single unit 3.5 ton. It comes out of the unit to 2 10inch ducts one 10inch duct supplies middle floor which supplies 6 vents and 1 return. Second 10inch duct feeds the upper floor which supplies 6 vents 3 returns and has another 10inch duct that extends from this one that feeds the bottom floor which supplies 4 vents and 1 return that is shared with the middle floor return.

  7. #7
    Join Date
    Feb 2005
    Posts
    5
    Post Likes
    Thread Starter

    to fat eddie

    it runs for about 10-15mins at a time. the thermostat and humidity control is on middle floor.

  8. #8
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    Are you saying 2 10" flex supply runs? If so you have real ductwork problems, need more like 2 10 x 12 metal trunklines. Tri-level's are hard to keep uniform temps, about all you can do is run the fan all the time. Did the old system work better?

  9. #9
    Join Date
    Feb 2005
    Posts
    5
    Post Likes
    Thread Starter
    there was no old system. My house was electric heat before. the 10inch duct work only runs for about 3 feet then its the hard square duct work and branches to the registers are 6 inch flex duct. Do you think that the fans that you can put in the 6inch flex duct really work to provide more airflow to the lower floor? Do you think the manual air control duct would work if it was put somewhere in the 6inch duct to the registers? I am not sure what this is called but it has a lever on the side that can block the air flow to the upstairs floor would it devert more air to the first floor. closing the regesters did not work.

  10. #10
    Join Date
    Jan 2005
    Location
    daytona florida
    Posts
    76
    Post Likes
    NO YOU HAVE DUCT PROBLEMS AIR FLOW AIR FLOW AIR FLOW

  11. #11
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    did you or contractor run load calc?
    read lots here --

    again, were you warm enuf with old system? is new furn same size as all baseboard addded together?

    did someone say: "air flow"

    how about assume 600sfpt?

    [Edited by cem-bsee on 02-19-2005 at 06:30 AM]

  12. #12
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,307
    Post Likes
    I agree with the guys. You have wrong sized duct(10") to feed the main trunk.

  13. #13
    Join Date
    Dec 2004
    Posts
    201
    Post Likes
    if you want it to work properly, i think you might have to start over

  14. #14
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Unfortunately if the unit is running a fifteen minute cycle it will point more to a problem in the duct design rather than some type of equipment problem. We have to go with the fact that the stat is on the middle floor and that is the only floor that the unit will listen to or care about the other floors can be considered slaves to the middle floor. If the system fails to condition the other floors satisfactorally, then you have a ducting issue which may or may not be as simple as balancing it out. More than likely you will need to have the ducting modified to bring the other floors to some type of balance with the middle floor.

  15. #15
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    I just caught the part about two 10" supplies this defies any air flow chart ever made for a normal residential static pressure ? unfortunately or maybe fortunately the centrifugal blower in your furnace will peak out on its curve without moving the sufficeint air. You should have noticed in the cooling season that your suction line may have froze. You have to find a way to get the proper trunk connected to this thing. Is this furnace a lot louder than the previous one ?

  16. #16
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    Originally posted by fat eddy
    I just caught the part about two 10" supplies this defies any air flow chart ever made for a normal residential static pressure ? unfortunately or maybe fortunately the centrifugal blower in your furnace will peak out on its curve without moving the sufficeint air. You should have noticed in the cooling season that your suction line may have froze. You have to find a way to get the proper trunk connected to this thing. Is this furnace a lot louder than the previous one ?
    He just had it put in so hasn't run in cooling, no old system - electric heat before.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •