Results 1 to 13 of 16
Thread: low air flow&humidity
-
02-18-2005, 08:20 PM #1
Regular Guest
- Join Date
- Feb 2005
- Posts
- 5
Having problem with air flow & humidity. I live in a split level rancher. Heater is in the attic .there is a 10 degree difference from lower floor to upper floor .starting at the lower floor 65/70/75. Humidifier can not keep up. There is a noticeable difference in air flow, upper floor to lower with the lower floor having the least.
-
02-18-2005, 09:01 PM #2
Professional Member
- Join Date
- Dec 2004
- Posts
- 198
sounds like a poor setup,,are you new to the house
-
02-18-2005, 09:09 PM #3
Regular Guest
- Join Date
- Feb 2005
- Posts
- 5
not new to the house. We just had a contractor install it.
-
02-18-2005, 09:17 PM #4
Professional Member
- Join Date
- Dec 2004
- Posts
- 198
are you saying there is one airhandler in the attic supplying 3 floors
-
02-18-2005, 09:31 PM #5
Banned
- Join Date
- Feb 2005
- Posts
- 1,475
How long of a cycle does the furnace run ?
-
02-18-2005, 10:35 PM #6
Regular Guest
- Join Date
- Feb 2005
- Posts
- 5
its a single unit 3.5 ton. It comes out of the unit to 2 10inch ducts one 10inch duct supplies middle floor which supplies 6 vents and 1 return. Second 10inch duct feeds the upper floor which supplies 6 vents 3 returns and has another 10inch duct that extends from this one that feeds the bottom floor which supplies 4 vents and 1 return that is shared with the middle floor return.
-
02-18-2005, 10:38 PM #7
Regular Guest
- Join Date
- Feb 2005
- Posts
- 5
to fat eddie
it runs for about 10-15mins at a time. the thermostat and humidity control is on middle floor.
-
02-18-2005, 11:07 PM #8
Are you saying 2 10" flex supply runs? If so you have real ductwork problems, need more like 2 10 x 12 metal trunklines. Tri-level's are hard to keep uniform temps, about all you can do is run the fan all the time. Did the old system work better?
-
02-18-2005, 11:37 PM #9
Regular Guest
- Join Date
- Feb 2005
- Posts
- 5
there was no old system. My house was electric heat before. the 10inch duct work only runs for about 3 feet then its the hard square duct work and branches to the registers are 6 inch flex duct. Do you think that the fans that you can put in the 6inch flex duct really work to provide more airflow to the lower floor? Do you think the manual air control duct would work if it was put somewhere in the 6inch duct to the registers? I am not sure what this is called but it has a lever on the side that can block the air flow to the upstairs floor would it devert more air to the first floor. closing the regesters did not work.
-
02-19-2005, 05:14 AM #10
Regular Guest
- Join Date
- Jan 2005
- Location
- daytona florida
- Posts
- 76
NO YOU HAVE DUCT PROBLEMS AIR FLOW AIR FLOW AIR FLOW
-
02-19-2005, 06:27 AM #11
Professional Member
- Join Date
- Feb 2003
- Location
- Huntsville,AL
- Posts
- 4,125
did you or contractor run load calc?
read lots here --
again, were you warm enuf with old system? is new furn same size as all baseboard addded together?
did someone say: "air flow"
how about assume 600sfpt?
[Edited by cem-bsee on 02-19-2005 at 06:30 AM]
-
02-19-2005, 10:49 AM #12
I agree with the guys. You have wrong sized duct(10") to feed the main trunk.
-
02-19-2005, 01:17 PM #13
Professional Member
- Join Date
- Dec 2004
- Posts
- 198
if you want it to work properly, i think you might have to start over