    Have been running across floating chilled water valves used as 2 position lately. Some say 2 positioning gets the whole coil cold and dehumidifies better, some say that's not true and uncomfortable. Why pay for a floater and not float it? Time to vote.

  2. #2
    Join Date
    Mar 2004
    Location
    Austin, Texas
    Posts
    1,982
    Post Likes
    Originally posted by incontrol
    Have been running across floating chilled water valves used as 2 position lately. Some say 2 positioning gets the whole coil cold and dehumidifies better, some say that's not true and uncomfortable. Why pay for a floater and not float it? Time to vote.
    Here is my vote - very, very, bad idea. By using a two position chilled water valve the system is made to function just like on - off control on DX cooling. It may do a better job of dehumidification while it is on, but when it shuts off it does NO dehumidification.

  3. #3
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,890
    Post Likes
    Go with MODULATING VALVE

  4. #4
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Terrible, thats why mod valves were made, now if you said you were leaving it open then reheating that is an ashrae cycle for dehum.

  5. #5
    Join Date
    Sep 2004
    Posts
    76
    Post Likes
    2-10 or 4-20, only use floating if you have to, and don't use on/off, IMHO

  6. #6
    Join Date
    Jul 2002
    Posts
    986
    Post Likes
    Thanks guys. I agree with modulation but almost always see on/off.

  7. #7
    Join Date
    Feb 2005
    Posts
    293
    Post Likes
    Sound like someone had a shop full of floating valves.