Results 1 to 11 of 11
Thread: york
    Feb 2005
    Frown
    I have been working on this unit for some time changed the defrost board , replaced the low pressure switch , added and removed charge . I replaced the pressure switch and resolved one fault code and then with I an half hour of opperation I gotanther fault code that said I was( reciving a single on w in the a/c mode) but we were in the heating mode ..... I checked the wires no short now Im going to replace the t-stat.. anyone with crazy **** like this like to know thanks
    Nov 2001
    When all else fails,
    replace everything.
    If you try to fail, and succeed.
    Which have you done ?
    Lancaster PA
    Got a M, and S number for that unit.
    I haven't run into that one yet.
    But, you might want to check for voltage on your orange.
    west chester pa
    sounds like you were in defrost mode.
    Feb 2005
    Unhappy
    the outdoor fan was not running and the only way the ornge is energized is the t- stat or outdoor board..I replacd the defrost board because it would not test defrost.
    west chester pa
    Exclamation
    Are you a homeowner????
    Feb 2005
    Confused
    no just starting in this trade
    Lancaster PA
    Some of them won't go in to defrost if the defrost sensor is bad.
    Feb 2005
    I tested the senser by temp and resis and it was good.
    Lancaster PA
    What m#, s#, of outdoor, and indoor unit, and what t stat are you using on it.
    Feb 2005
    Talking
    just had the york people here today hope the problem is resolved. The only thing wefound was the way the humid was hooked up, rewired the unit with a current sensing relay and the home owners wonted the same t-state that thay put on. So thay got a honeywell with a york name. Now I hope I dont see them till there PM.thanks for all the help
