Page 2 of 2 FirstFirst 12
Results 14 to 19 of 19

Thread: york

  1. #14
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    The ceiling ambient was pretty close to the room below it was not a factor.return grills are in the drop ceiling tiles just no ductwork attached this isn't that uncommon, and the new unit works fine.

  2. #15
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    2,731
    Post Likes
    Originally posted by fat eddy
    The ceiling ambient was pretty close to the room below it was not a factor.return grills are in the drop ceiling tiles just no ductwork attached this isn't that uncommon, and the new unit works fine.
    I'm sure the temps were close with open ceiling grills using the ceiling as return. Kind of like using the attic at home for a return, try doing a load calc with and without the ceilng as a buffer zone. Why wouldn't you do the installs or service under warranty? York won't let you?

  3. #16
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,868
    Post Likes
    Using the space between the firerock and the suspended ceiling for return is common. All commercial work in my area is this way and designed by engineers. The insulation is above the sheetrock. This would have nothing to do with his problems.

  4. #17
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    2,731
    Post Likes
    Originally posted by trane
    Using the space between the firerock and the suspended ceiling for return is common. All commercial work in my area is this way and designed by engineers. The insulation is above the sheetrock. This would have nothing to do with his problems.
    I don't think Eddy's got a double 2 hour fire rated ceiling if the Air handler is less than 5' from the condenser on the roof. Don't forget the York rep condemned the install and voided the warranty.

  5. #18
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,868
    Post Likes
    Smith, you may be right. I would hate to think they would install it any other way.

  6. #19
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Our company does not install equipment, we sell it to contractors and sometimes direct to customers if we sell direct to a customer we sub out all the trades, have a factory start-up then respond to service calls if the call is a problem with the equipment we call the factory in to service it.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365