Hello
I've got a Majestic HE25RN natural gas insert which recently started having a problem. The pilot light stays lit but when I turn on the switch to produce flame nothing happens. The switch contact is OK.
Any idea/suggestions on what is causing this problem??
-
02-15-2005, 07:54 PM #2
fireplace
try to turn the gas valve to the on posistion.
GOOD WORK IS NOT CHEAP! AND CHEAP WORK IS NOT GOOD!
IF YOU THINK A GOOD HVAC COMPANY IS EXPENSIVE. THEN YOU SHOULD TRY A BAD ONE.
-
02-15-2005, 08:10 PM #3
Regular Guest
- Join Date
- Feb 2005
- Posts
- 102
what kind of switch is it ,jump the switch.
-
02-15-2005, 08:14 PM #4
Regular Guest
- Join Date
- Jan 2005
- Posts
- 99
Rauchen, the millivolt reading at the gas valve needs to be at minimum 300 m.v. to actuate gas valve. Im assumming this is a millivolt system? If you find a lower reading than 300 m.v. check pilot and or pilot generator and clean or replace as neccessary.
-
02-15-2005, 08:16 PM #5
Professional Member
- Join Date
- Jun 2003
- Location
- New Hampshire
- Posts
- 2,663
When this happens the pilot is usually strong enough to keep the pilot energized but if the pilot is a little dirty the millivoltage is not enough to energize the main valve. There is a voltage drop in the wire to the switch and back again.
We are talking millivolts here.
You can post this on the "fireplaces section" too for more replies.