    Re : Charging

    No matter which alternative Refrigerant you use, you charge 80% of the factory charge. Also these alternatives are near zeotropic mixture so you will have flashing in the sight glass
    RAM Teaching Tomorrows Technicians Today.

  2. #22
    Join Date
    Aug 2001
    Posts
    200
    Post Likes
    Thread Starter
    Unit was setup for a semi-hermetic and 404-a, The existing compressor was setup with poly oil. and Hotshot. I installed new filters both suction and liquid, flushed the system with FX11 and purged with nitrogen, Leak tested with nitrogen and R22. Evacuated to 500 microns, and used R404-a, and all is well... Down to 38 degrees.

  3. #23
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes

    Re: Re : Charging

    Originally posted by icehouse
    No matter which alternative Refrigerant you use, you charge 80% of the factory charge. Also these alternatives are near zeotropic mixture so you will have flashing in the sight glass
    The reason for bubbles in glass is cuz you're actually shortcharging the unit. And actually if you have glass, you have a TXV, which means you have a receiver, which means you should have a solid column. Adjust your TXV clockwise (increase superheat) for the drop-in you are using. Change powerheads, whatever. And before anyone gives me shit, it's worked for years for us with fewer comp failures than others.
    With cap tubes you still have to shortcharge it.


  4. #24
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes

    Re: Re: Re : Charging

    Originally posted by jerrycoolsaz
    Originally posted by icehouse
    No matter which alternative Refrigerant you use, you charge 80% of the factory charge. Also these alternatives are near zeotropic mixture so you will have flashing in the sight glass
    The reason for bubbles in glass is cuz you're actually shortcharging the unit. And actually if you have glass, you have a TXV, which means you have a receiver, which means you should have a solid column. Adjust your TXV clockwise (increase superheat) for the drop-in you are using. Change powerheads, whatever. And before anyone gives me shit, it's worked for years for us with fewer comp failures than others.
    With cap tubes you still have to shortcharge it.


    No one should give u any "shit". In the first place "You can't argue with success". In the second place in the 40 some years i've been in this field I have never found an expansion valve that worked properly without a full column of liquid entering it.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  5. #25
    Join Date
    Dec 2003
    Location
    Lafayette, Ind.
    Posts
    13
    Post Likes
    System proulby used R-12, check TXV, it should give you an indecation. For R-12 I sub R-409a It will mix with polyester, minural or alkabenzene oil.
    Good luck

  6. #26
    Join Date
    Feb 2005
    Posts
    69
    Post Likes

    Re: Re: Re: Re : Charging

    Originally posted by rayr
    [i]

    No one should give u any "shit". In the first place "You can't argue with success". In the second place in the 40 some years i've been in this field I have never found an expansion valve that worked properly without a full column of liquid entering it. [/B]
    ...........So, I guess when it comes to these new refrigerants we should throw away the old rule book. Yes, there should be a full column of liquid refrigerant going to the txv, atleast with R22,R12,R502 etc. All the original refrigerants.

  7. #27
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,880
    Post Likes
    I prescribe to the full column of liquid theory. Think volume, not weight when charging new gases.
    A Diamond is just a piece of coal, that made good under pressure!

  8. #28
    Join Date
    Feb 2005
    Posts
    69
    Post Likes
    Originally posted by frozensolid
    I prescribe to the full column of liquid theory. Think volume, not weight when charging new gases.
    ...On mt P.T. chart for "hotshot" it says not to clear the glass...go figure......??

  9. #29
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes
    [QUOTE]Originally posted by tech cr
    ...On mt P.T. chart for "hotshot" it says not to clear the glass...go figure......??
    Because Hotshot is sold as drop in. You as a tech should know what is happening when you have 'bubbles' in the glass. What's going to happen if the load increases substantially in the box? What's happening to compressor superheat?

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •