Page 2 of 2 FirstFirst 12
Results 14 to 19 of 19
  1. #14
    Join Date
    Feb 2007
    Location
    Baltimore MD ( Balimer, Murilyn)
    Posts
    148
    Post Likes
    I believe the factory bearing clearances are listed in the SOM. If you've ever torn down a 19D series low pressure machine, you have a pretty good idea what to expect.

  2. #15
    Join Date
    Mar 2007
    Posts
    93
    Post Likes
    Quote Originally Posted by fmserviceteam View Post
    I need to check all bearing thrust and I dont have documentation to find allowable tolerance
    Here it is.

  3. #16
    Join Date
    Jun 2011
    Location
    San Jose, CA
    Posts
    126
    Post Likes
    5 years seems a little early. Maybe just do a front end now but even that may not be necessary. The best thing to do is take an oil sample and see what shows up in the oil. If there is no tin in the oil then chances are your bearings are fine. Leave it sealed unless there is a real reason to mess with it at this point. Once the hours get really up there then you could consider doing it for exploratory reasons.

  4. #17
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,198
    Post Likes
    Quote Originally Posted by fmserviceteam View Post
    Hello Johny I need your help. Please can you send me overhaul book for Carrier 19XR. I have disassemble compressor and I need documentation.
    Thanks in advance


    holy cow., you already took down the compressor and now you ask for help , manual ?!!?
    what am i missing., or shall I say what are you missing?
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  5. #18
    Join Date
    May 2012
    Location
    California
    Posts
    530
    Post Likes
    You can find the tol in the IOM manual use 19XL teardown book. I go off of oil sample depending on type of load chiller runs at and Carriers wonderful design with no rear motor bearing your low speed is ussally done also. Take it down and put new bearings in regasket it.

  6. #19
    Join Date
    Sep 2011
    Location
    BAJA AND CALIFORNIA
    Posts
    101
    Post Likes
    before teardown , you need to check the following:
    take oil sample of the unit and see what is the oil condition
    how many operation hours of the unit (very important)
    perform a vibration analisys (very important)
    before open the machine will be better make a prediagnostic

    regards

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.