Results 1 to 4 of 4
  1. #1
    Join Date
    Jan 2010
    Posts
    101
    Post Likes

    Flexible Duct Damper

    We have a 2 year old home with insulated flexible ducts from the plenum to the registers. Is it possible to install manual dampers in these ducts? The number 6" is written on the outside of the duct insulation. I assume that's the size of the flexible duct.

    Is the flexible duct cut, then a damper inserted and joined with the ends of the cut flexible duct?

    I'm trying to better balance our system for winter usage.

    Thanks.

  2. #2
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    2,670
    Post Likes
    put the damper where the flex leaves the box. This will keep noise down. You can put the damper in the collar.
    Doug

  3. #3
    Join Date
    Jan 2010
    Posts
    101
    Post Likes
    Thread Starter
    Thanks gunslinger.

  4. #4
    Join Date
    Jan 2010
    Location
    Athens GA
    Posts
    1,232
    Post Likes
    Its hard to say much without seeing some pictures but if you are having problems with airflo I'm willing to bet that its the flex causing the problems.
    Most people plan for about 100 cfm s coming to their registers.You would be lucky to get 75 cfms with 6" flex.Even if its installed right you would have to go up tp 7".
    Flex should be as short as possible,stright as an arrow,hung properly,and bends should be sheet metal.
    AS Gunslinger said,the take off s should be metal and a damper installed in that.
    The best system would be all metal and insulated on the outside.
    Your other problem is the return air.I can't see it but I'll bet its too small .Also a central return will not make remote room comfortable.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.