Thread: Low ambiant control on Trane split systems

  1. #1
    Join Date
    Nov 2009
    Posts
    28
    Post Likes

    Low ambiant control on Trane split systems

    Hi,

    Can somebody tell me if low ambiant control on Trane split systems are reliable for winter severe cold weather (0F). I want to make sure that it will work all the time for offices where no free cooling is available.
    Am I better to go for refrigeration condensers (like Ref Plus) to be safe.

    Thanks
    Alex

  2. #2
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Quote Originally Posted by alupien View Post
    Hi,

    Can somebody tell me if low ambiant control on Trane split systems are reliable for winter severe cold weather (0F). I want to make sure that it will work all the time for offices where no free cooling is available.
    Am I better to go for refrigeration condensers (like Ref Plus) to be safe.

    Thanks
    Alex
    Its done all the time commercially, it is generally more than just adding a fan cycling control and calling it done though.....

    Things like hot gas bypass accompanied by some times a desuperheater, defrost stats on the evaporator, a manual reset freeze stat that might have to be changed to an auto reset, low pressure bypass TDR, etc.

    Really depends on the application as to what job gets what.

  3. #3
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    Post Likes
    Quote Originally Posted by alupien View Post
    Hi,

    Can somebody tell me if low ambiant control on Trane split systems are reliable for winter severe cold weather (0F). I want to make sure that it will work all the time for offices where no free cooling is available.
    Am I better to go for refrigeration condensers (like Ref Plus) to be safe.

    Thanks
    Alex
    We use Trane head presure control kit all the time. U set what temp you want to keep the Liquid line. The board then measures the liquid line temp and ambient air temp..does some math and cycles the Fan. They also work on Heat pumps where its basically bypassed when the unit is in "heat" mode. Stated one up Thursday..was 15 deg out. Fan would do a quarter turn about every 20 seconds. I would also add a crank case heater.

  4. #4
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    you can also just put a Penn adjustable fan cycling pressure switch, set it to keep fan on at 250 and off at 200

  5. #5
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by yellowirenut View Post
    We use Trane head presure control kit all the time. U set what temp you want to keep the Liquid line. The board then measures the liquid line temp and ambient air temp..does some math and cycles the Fan. They also work on Heat pumps where its basically bypassed when the unit is in "heat" mode. Stated one up Thursday..was 15 deg out. Fan would do a quarter turn about every 20 seconds. I would also add a crank case heater.
    the smartest sure way to do it.

  6. #6
    Join Date
    Jul 2009
    Location
    new york
    Posts
    928
    Post Likes
    Quote Originally Posted by yellowirenut View Post
    We use Trane head presure control kit all the time. U set what temp you want to keep the Liquid line. The board then measures the liquid line temp and ambient air temp..does some math and cycles the Fan. They also work on Heat pumps where its basically bypassed when the unit is in "heat" mode. Stated one up Thursday..was 15 deg out. Fan would do a quarter turn about every 20 seconds. I would also add a crank case heater.
    What about hot gas bypass valve?

  7. #7
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by bwd111 View Post
    What about hot gas bypass valve?
    why open the refrigerant system?

  8. #8
    Join Date
    Aug 2007
    Location
    South central WI
    Posts
    257
    Post Likes
    Capacity control?
    The more I learn the smarter I work.

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Alex

    Is this the same unit from here?
    http://hvac-talk.com/vbb/showthread.php?t=702061

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •