    when homeowner finishes basement and bulids a closet for the furnace and water heater, would this rule apply
    50 cubic feet per 1000 btu's of air-space for combustion before having to bring in a combustion air pipe?
    or does that only pertain to water heaters, and natural draft furnaces?
    Thanks.
    "I'm not going to tip-toe through life, only to arrive safely at my death"

  2. #2
    Join Date
    Jan 2005
    Location
    daytona florida
    Posts
    76
    Post Likes
    ya fraid so

  3. #3
    Join Date
    Oct 2001
    Location
    Waterford Michigan
    Posts
    2,699
    Post Likes
    There may be other options I would have it evaluated by a licensed contractor.

  4. #4
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    3,419
    Post Likes
    You can put in high and low vents to still get combustion air from the finished basement.

  5. #5
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    Assuming that closet means standard type ( small room ) Then there is no scenario that will not require fresh air pipe besides a louvered door to an area that meets the equation you wrote in your

    first post, then the louver has to about 1 sq. in. free space for every 1,000 BTU

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •