Results 1 to 8 of 8

Thread: TStat ?

  1. #1
    Join Date
    Feb 2005
    Posts
    12
    Post Likes
    I have a 93% efficient furnace and 14 seer AC unit. Everyting seems to work fine but my furnace only runs 3-5 minutes at a time it does maintain the 70 degrees set on the furnace no problem. I have a Honeywell Chronotherm 111 thermostat. I was told it really causes the furnace to cycle to frequently. Any suggestions on a Tstat for this. It appears White Rogers Tstats will let you adjust temperature variance which will let the furnace burn longer. It seems to me the furnace is not near as efficent when it only burns 3-5 minutes. Just when the ductwork etc is warmed up it shuts down. Maybe I am wrong. Your thoughts will be greatly appreciated.

  2. #2
    Join Date
    Jan 2005
    Posts
    340
    Post Likes
    Originally posted by hageman6
    I have a 93% efficient furnace and 14 seer AC unit. Everyting seems to work fine but my furnace only runs 3-5 minutes at a time it does maintain the 70 degrees set on the furnace no problem.
    Your furnace looks oversized from here. Was a heat loss calculation done when it was installed?

  3. #3
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,794
    Post Likes
    The cycle rate for high efficiency furnaces on Honeywell stats can differ from the normal setting. Have your installer read the thermostat's installation literature to ensure which cycle rate is best for this system.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  4. #4
    Join Date
    Feb 2005
    Posts
    12
    Post Likes
    Thread Starter
    Yes the heat calc was completed. I had a 100BTU 80 percent that when operating really kept the house comfortable. The new 93 Percent efficnet furnace is an 80K based on the heat calc.

  5. #5
    Join Date
    Nov 2002
    Location
    Albuquerque, NM
    Posts
    35
    Post Likes
    I had a Honeywell T8000C Tstat installed with a new Carrier 58CVA furnace. The default cycling rate on the thermostat was 6 cycles per hour, while the furmace manual called for 3 cph. You need the tstat installation manual to know how to reset the tstat cycling rate. The owners manual doesn't have it! I reset it and it's much better. Obviously at 6 cph it's going to be cycling every 10 min which is annoying.

  6. #6
    Join Date
    Jan 2005
    Posts
    340
    Post Likes

    Cycle Rate adjustment on Chronotherm III


  7. #7
    Join Date
    Feb 2005
    Posts
    12
    Post Likes
    Thread Starter
    Thanks for the installation guide. It appears that this adjustement should take care of my problem.
    Thanks

  8. #8
    Join Date
    Jan 2005
    Posts
    340
    Post Likes

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums