    Goodman furnace "pressure switch stuck open"

    Had service out yesterday to work on the furnace. No heat, trouble light said "Pressure Switch Stuck Open." He replaced the pressure switch and also fixed some wires leading to it that had bizarrely got charred. (Not near the burner, not near a furnace panel, very strange.) In any case, it's still not working right. Power cycling the unit from the breaker panel seems to clear the condition (until it happens again.) Control board? Ghosts? Voodoo curse?

    Also, is there some kind of guarantee policy on HVAC service work? Do I get a credit on the original 1hr labor charge for the 2nd visit, or what?

    SirWired

  2. #2
    Join Date
    Nov 2010
    Location
    Kansas
    Posts
    2,705
    Post Likes
    All companies are differnt...if we were out yesterday and it is still not working right then we consider it a Call Back and go back for free to do a correct dianosis and when we figured out the correct problem then we would work out pricing or refund or whatever the case might be.

    Good idea to ask this when having a company out.
    .


    The statement below is my signature and just my overall feeling towards our industry and does not necessarily pertain to you nor this thread.


    There really isn't a legitimate excuse for not doing the job correctly!

  3. #3
    Join Date
    Apr 2010
    Location
    Arizona
    Posts
    192
    Post Likes
    I've had nothing but problems with Goodmans. Unfortunately you just may have to bite the bullet and pay the piper to troubleshoot your unit because even though Goodmans have a labour warranty if you buy into it when you purchase a unit from them, it is hard for any tech or company to get reimbursed for time spent troubleshooting defective Goodman units. Been there and done that!

    I don't know what to tell you here. Goodmans are full of chinese parts that don't play well together and them being branded as "Designed, Engineered and Assembled in the USA" is a total joke since they are made mostly out of chinese parts.

    How old is this furnace? The installer should be the one looking at it. Charred wiring scares me but then so do Goodmans.
    I would remind you that extremism in the defense of liberty is no vice! And let me remind you also that moderation in the pursuit of justice is no virtue!

    The late and greatest ever, Senator Barry Goldwater

  4. #4
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Call backs don't cost the customer anything if the problem was improperly diagnosed.

    If the pressure switch truely failed and another componet now is acting up then it's not a call back. If the pressure switch was doing it's job and the tech didn't test it correctly then it is a call back.

  5. #5
    Join Date
    Dec 2005
    Posts
    2,032
    Post Likes
    Quote Originally Posted by mrbenz7 View Post
    I've had nothing but problems with Goodmans. Unfortunately you just may have to bite the bullet and pay the piper to troubleshoot your unit because even though Goodmans have a labour warranty if you buy into it when you purchase a unit from them, it is hard for any tech or company to get reimbursed for time spent troubleshooting defective Goodman units. Been there and done that!

    I don't know what to tell you here. Goodmans are full of chinese parts that don't play well together and them being branded as "Designed, Engineered and Assembled in the USA" is a total joke since they are made mostly out of chinese parts.

    How old is this furnace? The installer should be the one looking at it. Charred wiring scares me but then so do Goodmans.
    Look around your house. How many items are made in china. Item you use to put in your mouth to the item you wipe your azzz with.
    Get used to it.

  6. #6
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    Quote Originally Posted by martyinlincoln View Post
    Call backs don't cost the customer anything if the problem was improperly diagnosed.

    If the pressure switch truely failed and another componet now is acting up then it's not a call back. If the pressure switch was doing it's job and the tech didn't test it correctly then it is a call back.
    Every job is different and in the original post "Charred" wires were replaced and therefore NEEDED to be done...i.e. no refund for work that needed to be done: However,

    As stated before, call them back out because it's still not working right and they will probably make adjustments if necessary.
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  7. #7
    Join Date
    Sep 2004
    Posts
    51
    Post Likes
    Thread Starter
    Well, I figured out the problem (caught it in the act of refusing to start before it gave up and posted the trouble light)... induction blower doesn't want to start without "percussive encouragement" (a.k.a. my MagLite.) It just sits there and hums and doesn't turn the blower wheel.

    *sigh* And the service place doesn't work weekends, so I'll just shepherd it through the next couple of days.

    SirWired

    P.S. This particular motor is Made in Italy.

  8. #8
    Join Date
    May 2000
    Location
    Urbandale IA. USA
    Posts
    5,456
    Post Likes
    Goodman units have 5 or 10 yr PARTS warranty.
    How old is this unit?
    Was it registered with Goodman?
    Can you tell us the mod # ?
    INTERMITTENT problems ARE sometimes difficult to diagnose.

    I have installed MANY Goodman units with less than 1% WARRANTY failures.
    The installation may be contributing to the failure of the part...
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.

  9. #9
    Join Date
    Mar 2010
    Location
    Spud Country
    Posts
    326
    Post Likes
    The company I work for installs Goodman. Like any other equipment I have installed they all have there problems. Over all they are not that bad if installed properly.
    I am an experienced, caring, trusted, service provider who solves my customers issues beyond there expectations by educating them and guiding them with value-building options to make excellent buying decisions while building security and wealth for my company, myself and my family.

  10. #10
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    Typical - tech sees pressure swith is open - IT MUST BE A BAD SWITCH! Not.
    You probably won't like the price on the new inducer. I would get the model and serial number, and check warranty status.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  11. #11
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by mrbenz7 View Post
    I've had nothing but problems with Goodmans. Unfortunately you just may have to bite the bullet and pay the piper to troubleshoot your unit because even though Goodmans have a labour warranty if you buy into it when you purchase a unit from them, it is hard for any tech or company to get reimbursed for time spent troubleshooting defective Goodman units. Been there and done that!

    I don't know what to tell you here. Goodmans are full of chinese parts that don't play well together and them being branded as "Designed, Engineered and Assembled in the USA" is a total joke since they are made mostly out of chinese parts.

    How old is this furnace? The installer should be the one looking at it. Charred wiring scares me but then so do Goodmans.

    You see all those places were you have the word "Goodman"? you could place any other brand name in that slot, and it would make no difference.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  12. #12
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    Once again, Mr. Bill hits the nail on the head.
    Goodman is no different from any other brand. Apologies to the Goodman, (or any other brand) bashers.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  13. #13
    Join Date
    Aug 2010
    Location
    Chicago, IL.
    Posts
    135
    Post Likes
    Quote Originally Posted by 2old2rock View Post
    Typical - tech sees pressure swith is open - IT MUST BE A BAD SWITCH! Not.
    You probably won't like the price on the new inducer. I would get the model and serial number, and check warranty status.
    If the pressure switch is open and there is no blockage and upon replacing the pressure switch, unit works fine, who looks further?

  14. #14
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    Who looks further? The guy that doesn't like to do call backs.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  15. #15
    Join Date
    Nov 2010
    Location
    Kansas
    Posts
    2,705
    Post Likes
    Quote Originally Posted by yucan2 View Post
    If the pressure switch is open and there is no blockage and upon replacing the pressure switch, unit works fine, who looks further?
    Maybe if it had just been the switch...but there was another issue, the charred wires. I don't know if the tech looked for a cause or not, but to answer your question...many techs would have looked past the switch in this case.

    Me and my guys would have looked further in this case, because of the charred wires...we would have wanted to know the cause of the charred wires. We would have been worried that if we just repaired the wires and not found the cause that we might have to go back.

    Kind of like replacing a blown fuse and not looking for a cause that might have blown the fuse.
    .


    The statement below is my signature and just my overall feeling towards our industry and does not necessarily pertain to you nor this thread.


    There really isn't a legitimate excuse for not doing the job correctly!

  16. #16
    Join Date
    Sep 2004
    Posts
    51
    Post Likes
    Thread Starter
    Well, the furnace was here when I bought the house, so I have no idea exactly how old it is, if it was registered, etc. It looks pretty new, and the servicer said that the dark-grey cabinet units were all fairly recent.

    Can somebody here help me out? The Goodman website can find the unit, but doesn't give me any other information.

    Model GMS80453ANA
    Serial 0409768867

    Thanks,
    SirWired

  17. #17
    Join Date
    Feb 2009
    Location
    Wisconsin
    Posts
    412
    Post Likes
    Thats a single stage, 80%, 45,000 BTU, with a 3 ton drive, built in September 2004. Overall, a decent furnace.
    You have to fight through some bad days to earn the best days of your life.
    You can learn something from EVERYONE.

  18. #18
    Join Date
    Dec 2010
    Posts
    1
    Post Likes

    Charred wires

    I would be concerned about the charred wires indicating roll out from a cracked heat exchanger. Make sure to get it checked as soon as possible.

  19. #19
    Join Date
    Aug 2010
    Location
    Chicago, IL.
    Posts
    135
    Post Likes
    Quote Originally Posted by Tech23 View Post
    Maybe if it had just been the switch...but there was another issue, the charred wires. I don't know if the tech looked for a cause or not, but to answer your question...many techs would have looked past the switch in this case.

    Me and my guys would have looked further in this case, because of the charred wires...we would have wanted to know the cause of the charred wires. We would have been worried that if we just repaired the wires and not found the cause that we might have to go back.

    Kind of like replacing a blown fuse and not looking for a cause that might have blown the fuse.
    Very good explanation. I had completely forgotten about the charred conductors.

  20. #20
    Join Date
    Apr 2010
    Location
    Arizona
    Posts
    192
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    You see all those places were you have the word "Goodman"? you could place any other brand name in that slot, and it would make no difference.
    We got it the 1st time. You do not like Goodman. But you are painting with a broad brand-bashing brush. Stay specific to the questions and save the slamming for the thread for in the Pub.
    Last edited by Stamas; 12-12-2010 at 06:33 PM. Reason: Brand Bashing
    I would remind you that extremism in the defense of liberty is no vice! And let me remind you also that moderation in the pursuit of justice is no virtue!

    The late and greatest ever, Senator Barry Goldwater

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •