    Yes I know. It's mostly crap

    Can't find my paper that came with it. I hook it up and wait till I think it has warmed up and start a vacuum. All I get on any scale setting is the bars flashing across. I did have the micron scale come up one time today but it went to 1250 and stopped. Gauges read 29+ inches.

  2. #2
    Join Date
    Mar 2003
    Location
    Cincinnati
    Posts
    7,977
    Clean the sensor James.

  3. #3
    Join Date
    Nov 2000
    Location
    Coastal Georgia
    Posts
    34,902
    Does anyone know how to clean the sensor?

  4. #4
    Join Date
    Feb 2001
    Posts
    35,838
    With a sensor cleaner.
    Hey cockroach, don't bug me!

    www.AskTheDiceman.com

    www.TheColdConspiracy.com

    www.Pennwood-HVAC.Com

    Bring Em Home....

  5. #5
    Join Date
    Feb 2002
    Location
    Flemington, NJ
    Posts
    156
    Use Alchol, leave it in for about 5 minutes, empty, and shoot some nitrogen through it.

    DHC

  6. #6
    Join Date
    Nov 2000
    Location
    Coastal Georgia
    Posts
    34,902
    So I remove the AUX cap...put alcohol place cap back on for 5 minutes and blow out?

  7. #7
    Join Date
    Dec 2001
    Location
    Chicago, N/W burbs
    Posts
    8,004
    Chuck it off the roof and buy a Thermal VacCheck analog gauge.
    R2B4BTU

  8. #8
    Join Date
    Mar 2003
    Location
    Cincinnati
    Posts
    7,977

    CONNECTING TO THE VACUUM SYSTEM
    The VG64 should only be connected to the vacuum system at
    the vacuum port. The "Auxiliary Port" is primarily for cleaning
    and should normally be closed with the supplied cap.
    CLEANING THE VACUUM SENSOR
    It is recommended that the sensor be cleaned periodically to
    maintain unit accuracy . Oil and other contaminants reduce the
    accuracy of the unit. Follow the instructions below for cleaning.
    Close the Vacuum port with the supplied cap.
    Open the Auxiliary port.
    Use an eyedropper to pour about 2 teaspoons of ordinary
    rubbing alcohol into the Auxiliary port.
    Close the Auxiliary port with the supplied cap. Both the
    Vacuum and Auxiliary ports should now be closed.
    Shake the DVG64 unit for about 10 seconds. A slight
    movement of the vacuum sensor in the case is normal and
    does not affect the internal connection in any way.
    Open both the Vacuum and the Auxiliary ports.
    Empty the alcohol, and air dry the sensor.
    Close both the Vacuum and the Auxiliary ports with the
    supplied caps when the DVG64 is not used. This prevents
    contamination of the sensor.








  9. #9
    Join Date
    Nov 2000
    Location
    Coastal Georgia
    Posts
    34,902
    Thanks!

  10. #10
    Join Date
    Feb 2001
    Posts
    35,838
    I think he just doesn't know how to use it.
    Hey cockroach, don't bug me!

    www.AskTheDiceman.com

    www.TheColdConspiracy.com

    www.Pennwood-HVAC.Com

    Bring Em Home....

  11. #11
    Join Date
    Nov 2000
    Location
    Coastal Georgia
    Posts
    34,902
    I'll bet you have never used one.