    I have a site that has several Intellipaks (Vintage 1994). They are VAV units with gas heat. They still have an older Tracer 100 BMS on the system. My question is about the gas heat. The units run 24/7, so MWU is not an issue, but I thought gas heat was enabled when DWU initiate stpt was reached. There are several units reacting different, but none ever bring on gas heat.
    They all appear to be to stop economizing and start to warm up the space just on recirculation. Some actually show mode as DWU, others still show mode as cool, but close off OA and start recirculating.
    Am I missing some setting in the unit or Tracer that is holding out the gas heat?
    Any suggestions would be appreciated.
    b-man

  2. #2
    Join Date
    Feb 2009
    Location
    New York
    Posts
    53
    It has been a number of years, but I had the same problem there is a setting in the HI that has to be enabled, don't remember what section, (menu)...Hope this helps...FRED

  3. #3
    Join Date
    Mar 2008
    Posts
    103

    Trane Intellipak DWU Help

    FREDIEFREON
    Have DWU and MWU enabled. Don't know if this is what you are refering to.
    Thanks for th reply
    b-man

  4. #4
    Join Date
    Feb 2009
    Location
    New York
    Posts
    53
    I will look to see if i still have the manual, I think I left it in truck when changed job. But can remember doing same thing you have done and there was another setting..FRED

  5. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,492
    Daytime Warm Up description:
    If the unit is in the Occupied Mode and the zone temperature as measured at the Daytime Warmup sensor is lower than the Daytime Warmup Initiate Temperature then the unit will switch from Occupied to Unoccupied Mode. fter the Occupied/Unoccupied relay has been energized, the economizer goes to minimum position and the inlet guide vanes go to 100% open (the supply fan remains on during this transition). After the inlet guide vanes are full open, the heat is staged to maintain the Occupied Heating Setpoint. The unit will operate in the Daytime Warmup mode until the temperature in the space reaches the Daytime Warmup Terminate Temperature. After this temperature has been reached, all heat outputs are disabled, inlet guide vanes go closed, and unit will switch back to the Occupied Mode and control to Occupied Setpoints.

    you also have to enable Daytime Warm Up and you have to give it Setpoints of Initiate and Terminate. You also need to designate a sensor for the unit to look at.

    trane is constantly changing the baords and programming so some of the above may or may not apply to you. the menus where these items are located also changes.

    good luck.
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  6. #6
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,833
    ofcourse Jay is correct!


    I have a few setup that way

    you do need to have a sensor telling you what return air or space temp is!

    the problem I had was that the unit has to communicate with all of the vavs to tell them to open so the vfd/igv can go to 100% before the heat would come on!

    I think the system or the engineering idea needs a little work?






    Quote Originally Posted by jayguy View Post
    Daytime Warm Up description:
    If the unit is in the Occupied Mode and the zone temperature as measured at the Daytime Warmup sensor is lower than the Daytime Warmup Initiate Temperature then the unit will switch from Occupied to Unoccupied Mode. fter the Occupied/Unoccupied relay has been energized, the economizer goes to minimum position and the inlet guide vanes go to 100% open (the supply fan remains on during this transition). After the inlet guide vanes are full open, the heat is staged to maintain the Occupied Heating Setpoint. The unit will operate in the Daytime Warmup mode until the temperature in the space reaches the Daytime Warmup Terminate Temperature. After this temperature has been reached, all heat outputs are disabled, inlet guide vanes go closed, and unit will switch back to the Occupied Mode and control to Occupied Setpoints.

    you also have to enable Daytime Warm Up and you have to give it Setpoints of Initiate and Terminate. You also need to designate a sensor for the unit to look at.

    trane is constantly changing the baords and programming so some of the above may or may not apply to you. the menus where these items are located also changes.

    good luck.
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  7. #7
    Join Date
    Mar 2008
    Posts
    103

    Trane Intellipak DWU Help

    jayguy
    I think these are setup like you described. DWU initiate/terminate set at 68/72, DWU/MWU enabled, space sensor wired to Heat Module.
    Like I said earlier, units are acting differently. One will actually display HEAT/DWU OCCUPY, others never show DWU mode, still show COOL. None ever show a transition from Occupied to Unoccupied. All of them will close economizer to minimum and eventually you see Modualtion (IGV) 100%, but never try to bring on gas heat. I am trying to test this sequence by raising the setpoints 74/78. So it appears the units are reacting to setpoints, just not fully following the DWU sequence.
    The customer wants to prove the gas heat works as described.
    I feel I am still missing something in the setup of unit or Tracer.
    Thanks
    b-man

  8. #8
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    Your units run 24/7 so like you said MWU is a nonissue. DWU is initiated when the coor building temperature drops below the DWU setpoint. Have you checked the HI to see what sensor the DWU is looking at and what the DWU setpoint is? Is the temperature falling below setpoint and the heat doesn't come on or is it possible that the VAV's are keeping the temperature above setpoint and the heat isn't calling?

  9. #9
    Join Date
    Mar 2008
    Posts
    103

    Trane Intellipak DWU Help

    Phisher
    DWU is looking at same sensor as MWU uses, wired diectly to the Heat Module. This sensor is not associated with any VAV, it is there just to monitor space temp. I am raising the setpoints above this space sensor reading, to try to test sequence.
    b-man

  10. #10
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,492
    a couple of things...

    1. before the gas heat comes on...the space temperature may rise naturally and so the heat does not need to come on

    2. perhaps there is a problem with the gas train (tripped safety, etc)

    3. run the unit in TEST mode and prove that the gas heat works
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  11. #11
    Join Date
    Mar 2010
    Location
    Va.
    Posts
    180
    Quote Originally Posted by b-man View Post
    Phisher
    DWU is looking at same sensor as MWU uses, wired diectly to the Heat Module. This sensor is not associated with any VAV, it is there just to monitor space temp. I am raising the setpoints above this space sensor reading, to try to test sequence.
    b-man
    It's true that the sensor isn't directly associated with any VAV. The DWU is only in play when the average building temperature drops below setpopint. If the temperature drops below setpoint the HI will switch the unit from VAV mode of operation to CV mode of operation to reheat the space. If the VAV's are doing there job and heating the space then DWU should never be initiated.

  12. #12
    Join Date
    Mar 2008
    Posts
    103

    Trane Intellipak DWU Help

    jayguy
    Already did a heating checkout of burners in test mode of all units. Left 2 units with raised DWU setpoints for 3 hrs and space never reached terminate setpoint, economizer at minimum, 100% IGV and no call for gas heating, and again only 1 actually displayed it was in DWU.
    Guys, I appreciate the input! It at least makes me feel like am not overlooking something obvious.
    b-man

  13. #13
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,492
    is there a problem with the space temp? or is this just a note while you were inpsecting the units?
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event