Thread: Attic HVAC Issue

  1. #1
    Join Date
    Feb 2005
    Posts
    4
    Post Likes
    We did an addition on our house and installed a two zone heat system with one of the HVAC units in a small room in our unfinished attic. There are insulated ducts in the attic also coming from the room for this system. The problem we are having is that we cannot get the temperature in the attic under about 40 degrees. We have added additional roof venting (both soffit and top of roof) with little effect. We want to get the temperature closer to the outside to prevent ice dams and condensation problems.

    The HVAC room is drywalled and has insulation. The ducts are insulated the flexible insulated variety (R-4?). It seems like the only explanation is that there is heat coming from the HVAC room or duct work. Any suggestions?

    Note: we live in Northern Illinois.

    Thanks!

  2. #2
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Originally posted by threeboys
    ...one of the HVAC units in a small room in our unfinished attic...
    What are you calling an "HVAC unit"?
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  3. #3
    Join Date
    Feb 2005
    Posts
    4
    Post Likes
    Thread Starter
    bwal2, it is a new Trane UX80 furnace. What do you think? Thanks.

  4. #4
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    5,598
    Post Likes
    Could be a loose duct


    May not be the duct at all, but heat loss from house, like air leakage out recessed lights or missing insulation.
    Col 3:23


    questions asked, answers received, ignorance abated

  5. #5
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Originally posted by threeboys
    bwal2, it is a new Trane UX80 furnace. What do you think? Thanks.
    Glad it's not a heat pump leading a sorry life in your attic.

    Insulate, ventilate, keep good insurance.
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  6. #6
    Join Date
    Feb 2005
    Posts
    4
    Post Likes
    Thread Starter
    Thanks, guys for the input.

    bwal2 -- alright, why do you say "keep good insurance"??? Don't like Trane or attic installations?

  7. #7
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Originally posted by billygoat22
    Could be a loose duct


    May not be the duct at all, but heat loss from house, like air leakage out recessed lights or missing insulation.
    Could very well be from the house, maybe the insulation is all messed up after the HVAC install. May not be conducting from the ductwork, but maybe the heat is leaking out of the duct work.

    Could be warm air leaking out of house even around the diffusers.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  8. #8
    Join Date
    Feb 2005
    Posts
    4
    Post Likes
    Thread Starter
    Carnak- What is the best way to seal up the diffusers and other penetrations? Can I use expanding foam around the diffusers or is there something better? Thanks.

  9. #9
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    If it is a small gap you could even use silicone.

    You already checked the duct sealing, there is not hot air leaking out of ducts?
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  10. #10
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    duct sealing

    Use special duct sealing mastic on duct joints. Can use foam or caulk at boots and penetrations. Keep in mind warmair supply leaks outside the thermal envelope cause massive negative pressure inside which can backdraft atmospherically vented appliances. I'd increase that duct insulation. Don't forget other attic bypasses such as around stink pipes, wiring chases, etc. Warning! Chimney clearances cannot be packed with insulation. Fire Hazard. Can and should be properly firestopped such as with sheetmetal and caulk.
    HTH

  11. #11
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Originally posted by threeboys
    Thanks, guys for the input.

    bwal2 -- alright, why do you say "keep good insurance"??? Don't like Trane or attic installations?
    Nothing wrong with Trane.
    No better, no worse than anybody else's.
    It's just simple economics.

    Water + attic = $$$$


    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  12. #12
    Join Date
    Feb 2005
    Posts
    31
    Post Likes

    Attic air handler

    Originally posted by bwal2
    Originally posted by threeboys
    Thanks, guys for the input.

    bwal2 -- alright, why do you say "keep good insurance"??? Don't like Trane or attic installations?
    Bwal,
    I am getting estimates to replace a one unit, one cold air return on a two story residence with a two unit system. Of the 4 estimates I have had, 3 want to put the air handler in the attic and only one suggests leaving the upstairs air handler on the ground and building a new return duct through the floors next to the existing supply duct.
    Are overflowing condensate pans your only resistance to attic units?
    Thanks

    Nothing wrong with Trane.
    No better, no worse than anybody else's.
    It's just simple economics.

    Water + attic = $$$$



  13. #13
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    The condensate pan must actually catch the water in order to do any good.
    It is very common to put the furnace in the attic.
    It is also very common to pay somebody to repair water damage.
    If the unit freezes up, ice could form on the piping between the indoor & outdoor coil.
    When that ice melts, it is anyone's guess as to where the water will go.
    Also, adequate access must be provided.

    Don't let somebody cram this into a corner.

    Just be sure you go into this with both eyes wide open.

    I haven't seen your house, and don't know your contractor. Just be sure you voice your concerns ahead of time.

    [Edited by bwal2 on 02-20-2005 at 06:45 PM]
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  14. #14
    Join Date
    Feb 2005
    Posts
    1,475
    Post Likes
    I think that if your attic is at 40 and you are causing ice dams that it is probably more of a sun issue that a heatloss through the roof issue.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •