Thread: Bad ignitor ?
-
02-08-2005, 06:51 PM #1
Regular Guest
- Join Date
- Feb 2005
- Posts
- 1
Hello -
I have an 8-yr old Armstrong Ultra SX 80 forced air gas furnace with Honeywell controls. My blower runs, but the furnace quit lighting last night. I tried some diagnostics that I found on this site, and what I have so far is:
1) I don't smell much gas, but that's probably due to the good airflow/draft.
2) My vacuum line is clear with no condensation. The vacuum is fairly light, so I tested with manual suction. I can hear the pressure switch activating, but still no ignition.
3) I hear no click from the spark ignitor. With an OHM meter, I get resistance through the 'sense' wire to the ignitor, but no change in resistance through the 'spark' wire.
Is the ignitor a likely candidate ?
Model # GUJ125D14-1A
Ignitor tag: Honeywell 204470DB
Thanks in advance for any advice.
-
02-08-2005, 07:18 PM #2
Not a DIY site. Sorry.
"If anybody can draw on the power, where do we put the meter?" - JP Morgan before pulling Tesla funding
-
02-08-2005, 08:30 PM #3
Professional Member
- Join Date
- Feb 2004
- Posts
- 2,597
when was the last time you had it serviced?
it could be many things, including a cracked or perforated heat exchanger(which is not healthy for anyone).
save yourself some time and money and call a pro, not only to find the problem, but to ensure the safety and efficiency of your furnace.
check with neighbors and family for a referral.
good luck
-
02-08-2005, 08:45 PM #4
Professional Member
- Join Date
- Oct 2003
- Location
- west chester pa
- Posts
- 343
sounds like abad diy vavle i had a couple go bad on that particular unit


Reply With Quote