Re: Let me try again
Originally posted by bornriding
Shop, Doc, Thank ya'll very much. I've enjoyed reading and discussing your replies.
Here is my second try at explaining what I mean.
I've always thought that the reason for conditioning the air in an area ( say a home ) was to mixed the existing air in the home with cooler air from tha a/c system, at a proper level ( cfm's ), which determines how fast ( or slow ) the air is 'mixed' ( for lack of better word ) and then returned to the unit.
To me, there were two factors in determining how long it would take a 'home' to cool down from the time the thermostat turned the unit on until the thermostat was satisfied. And they were, the amount of cool air delivered to the home ( and recirculated within ) and #2 - the temperature of that air that was delivered.
I'm talking the same home, whatever the heat gain.
So, I've got a certain home, with a certain heat gain, and say my unit is sized correctly.
I kinda, at this moment, don't consider humidity or latent heat because by the time the air is delivered to the home from the system, only sensible heat is being sent.
I'm also not talking about the effects on a system from raising or lowering the volume of air or the temp. of the air.
But, to me, the amount of air and the temperature of that air are the two factors that actually govern the time that the a/c system will have to run to 'satisfy the thermostat'. And if I can get more air from a system, and maintain the same temperature of the air then the effect will cool the area ( home) quicker at less expense ( electric bill )
Or, if I cannot get more air, but if I lower the sensible temperature of the same air that is now being delivered to the home, then the effect will cool the home quicker at less expense. ( realizing that too much of either one is bad )
One of my points, I guess, is that all I here about how to set up a system deals with 'superheat' and yet, everyone gives a range of values, such as 10 to 15 degrees superheat ( + - 5 ).To me, the difference between 10 & 15 degrees superheat is a difference in the supply air temperature ( I have done tests for this ). If I set a system at 15 degrees superheat, the supply air will be (say) 59 degrees. But by setting the superheat at 10 degrees, the supply air reduces to (say) 55 degrees. So I prefer to set a system at 10 degrees s/h so that my supply air temp will be lower.... and I actually think that I am doing right.
All this, knowing of course that I must be careful to avoid liquid getting to the compressor.
What's ya'lls thoughts??
I think your confusion is based on a misunderstanding about types of heat in the space.
Latent heat: heat that causes a change of state not temperature. (Humidity)
For example it takes 970BTU’s of heat per pound to change water to steam at 212° F.
Sensible heat: is measured by a thermometer (heat intensity).
O.K. I know that was basic so here goes the explanation: Air conditioning systems need to remove total heat (latent plus sensible) or a total amount of BTU’s, if you want to look at it that way, at a greater rate than the heat gain.
The temperature of the air delivered to the home helps lower the sensible heat which the thermostat is measuring. You are correct in assuming that if the air volume is in creased and the supply air (SA) temp is lowered (over sizing the system in a sense) that the home will cool off quicker, but it will only cool off quicker sensibly. Once the sensible temperature requirement is satisfied at the thermostat then the unit cycles off. Now the latent heat in the space begins to “emit” and causes a rise in sensible heat and the unit starts again. It quickly removes the necessary sensible heat and cycles off. This cycle takes a relatively short amount of time so the unity cycles several times per hour in this yo-yo effect of trying to remove total heat. Multiple starts are undesirable.
Each start of the compressor does several things:
1. Causes an amperage spike (pulls locked rotor amps) which uses about five times more energy than just running
2. Heats up the windings in the compressor which rely on cool suction gas to cool off. So the unit cools off the space fast and shuts off with hot windings because the unit did not run long enough to get cool gas back to the compressor. Then in 5 min when it starts again the windings heat up more without being cooled off then the cycle repeats itself until the compressor fries itself.
3. The heat is also not good for the compressor oil which begins to break down and circulates through the system as sludge.
A properly sized system needs to remove sensible and latent heat (total heat) to be effective. The operation of a properly sized system goes something like this:
1. There is a call for heat.
2. The unit cycles on and begins removing total heat
3. Due to the run time of sufficient length the compressor windings are adequately cooled by the cool suction gas and the space has been properly dehumidified (latent heat removed).
4. The stat is satisfied and the unit cycles off and the unit stays off for a lengthier amount of time than if sensible cooling alone is used to cool the space so less starts = less energy consumed and better savings.
Super heat is a safety factor and is a preference setting to some degree it depends on the risks you are willing to take. The lower you go the more risk of loosing a compressor but more efficient. I have seen several systems run through our hot summers with only 8° of superheat and they are over 20 years old with the original compressor this definitely is on the low end of the superheat spectrum and merely my observation not a recommendation.
Load calculations are tried and true and are based on some really intense engineering research that you can trust. If the load calculations are performed correctly and the unit is installed correctly and kept clean then you will have a very efficient system. I realize these are two big ifs but that is my spiel hope it helps some.