Results 1 to 9 of 9
    Feb 2005
    I've inherited a job with VAVs that have been retrofitted with electronic controllers. They still have pneumatic damper acuators with a range of 5-10 psi. The transducers output 8-13 psi. Is this an acceptable way to do this or should the actuators have been matched to the output range of the transducers?
    Aug 2000
    Under my tree
    Cant you adjust the transducer to match the actuator spring range?
    To much work with too little time!!!!
    Feb 2005
    Where it's dark & damp
    I wouldn't think so. I would hope you could scale the transducer. I would think it was a little backwards to retrofit a pneumatic transducer considering the fact that an electronic VAV sized actuator would be around the same price if not cheaper than the transducer. The only exception I would think of would be the older Trane brand boxes with the globe style air valve and the pneumatic "baloon" style dampers where there would be no practical solution other than replacing the box or a transducer.
    Feb 2005
    The transducers are CP-8551 by seibe/invensys and I don't think they are adjustable, at least there's nothing in the accompining paperwork to say so.
    Feb 2005
    You're going to have to change something.If we're
    talking a Kreuter vav box or similar,they have 8-13
    actuators.Or return your xducers for a model with adjustable start point[lessen learned:always buy the
    convertible xducer,avoid the ah shit].Also if you are
    stuck,check all the damper actuator mngrs,somebody will have an 8-13 that will fit.
    If the spring range is 5-10 # and the dampers are set for this spring range then that makes the mid position at7.5# So if the transducers start at 8# then as soonas theyget there and supply this pressure to the motor it will go to just pass mid position. You will have the same problem coming the other way So the solution is to change the springs or the transducers.
    Jul 2001
    Canada
    What are you using to control the transducers, is it a INVENSYS controller ?
    The older CP 8551's had a bit of adjustment in them.
    Jul 2002
    Johnson has somthing like a "sequencing cumulator" etc.. It has a little spring inside you can adjust to counteract the higher pressure and change 8-13 into 5-10.
    do those transducers have internal feedback? if not you may be able to lower the air supply to that area and get half decent results until you can get the customer to spring for the new actuators.