Results 1 to 7 of 7

Thread: most efficient

  1. #1
    Join Date
    Mar 2004
    Location
    Southern ca
    Posts
    19
    Post Likes
    Which is more efficient in a residential home? two 2 ton split units or one 4 ton unit? If you were to keep the temperature in both zones the same. Just wondering. What are the pros and cons of two versus one unit.

  2. #2
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    2 units= likelyhood of not 2 broken at same time, usually cost more up front; can operate independent of each other. 2 cost more for regular maintenance -- 2 should match loads better, say one for bdrm, one for else --

    more efficient to have unit running full load.

  3. #3
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,068
    Post Likes
    Also considder the SEER ratings of 2 through 3.5 ton systems tend to be much higher than with 4 and 5 ton systems of a similar product line.
    RSES Certificate Member
    RSES-SWRA President

    You're not finished learning until you're dead!

  4. #4
    Join Date
    Sep 2002
    Posts
    4,979
    Post Likes
    Its going to cost more for 2- up front but thats the way I would go. Even tho your keeping it the same temperature the heat gain and loss is going to be differant from one part of the house to another so with 2 units it will be a little more even. Also depends on a little of how you divide it up with 2- units, up & down or split in half. Not sure what style house it is? I unit costs less.

    [Edited by dec on 02-07-2005 at 12:47 PM]

  5. #5
    Join Date
    Oct 2003
    Location
    west chester pa
    Posts
    348
    Post Likes
    2 heads are better than 1

  6. #6
    Join Date
    Nov 2000
    Location
    Memphis TN USA
    Posts
    6,969
    Post Likes
    Based on the original question
    2 2-ton units are supposed to have the same efficiency as 1 4-ton unit.

    You would get 2 units for other reasons than efficiency
    If the superheat ain't right it ain't charged right.

  7. #7
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Thats right, 48,000 btuh's produced at X SEER either by 2 units or one should be the same assuming the SEER rating is a system rating and not a coil only rating.

    That of course has nothing to do with comfort, control, installation costs or repairs.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.