    Confused Trane Voyager gas pack

    I wondering if anyone has any info on the ignition control a Trane M/N# YCD241C4HNCB S/N 904100804D
    the ignition goes through normal paces the inducer motor starts in high the burner lights runs for about a min then the inducer drops down to low speed it will run for about another min then the board will drop it all out I do not lose the call for heat and the board does not go into a lockout I check the d/c voltage on the pins for the flame sensor and never drops below 7.79 until after the gas valve drops out I do not lose 24v through TCO1 or TCO2 or through the automatic high temp sensor
    I talked to a trane tech support and I think I stumped him if anyone has any input please let me know what you think
    Thanks

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    are you using this


    do you have the reliatel manual?
    Last edited by dandyme; 01-07-2011 at 07:16 PM.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Feb 2004
    Location
    South Carolina
    Posts
    11
    as usual I post before I searched for other threads on the subject I found a couple of threads were links were posted for more info I got that one and several others & put them on my thumb drive plan on going back up there and go at it again with the new info
    Thanks alot for the response I'll update on what I find

  4. #4
    Join Date
    Dec 2010
    Location
    Va
    Posts
    89

    trane rtu

    Is the unit coughing an woofing? R u checking dc microamps,at the two test pins on the bottom of the ignition mod? It senses
    flame through the hot surface ignitor.

  5. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,390
    does cycling power make the problem go away?

    there was a service bulletin for a similar situation..but it was supposed to be fixed on units by serial numbers beginning with 827. perhaps yours slipped through or the problem is bigger than they originally thought or you got a replacement board before the fix from a parts distributor.

    call the local Trane office and ask for: RT-SVB35A-EN

    the service bulletin describes a field modification for the existing board.

    as always, make sure that the RTRM board is the latest version...i think it is up to version 8.'something' now...it may be higher. the RTRM board is the almighty board, and yes, it can affect the ignition board.
    When I am late for work, I usually make up for it by leaving early.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event