    I have one HVAC unit in the unfinished basement that is giving not enough cooling or heating upstairs (nothing in some places). Contractor suggsted upsizing the unit to 100K BTU from 80K BTU and 31/2 ton to 4 ton A/C. ALso, the ducting is not done right by the builder.

    I thought of setting up zoning because we don't need cooling or heating same time upstairs and downstairs. But there are two trunk line going out from the unit (one on either side) that supply to first and seconf floor (all mixed up both sides, i.e, alternately feeding first and second floor). I would like to run two trunk lines on each side supplying first and second floor separately so that they can be controlled by dampers. Since the basement is unfinished, I thought this can be done easily.

    Just upsizing furnace is $4K and system is $6K (no duct work)? I think it is too much. Quote for second unit in the attic (Heat pump and 2ton A/C is $6K)? My house is about 3200 sq ft and is only 5 years old.

    Thanks for any suggestions and recommendations.

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Have a load calcualton done ,to be sure your system is large enough.Other than that and being sure the duct are sixed right and there is space for them,it's a good idea.

  3. #3
    Join Date
    Aug 2001
    Posts
    209
    Since the basement is unfinished you may be able to zone it with a Arzel system. You just need to find out where all the supplys are going from the basement. Then you would be able to zone it for both floors.