    when i am talking to a hvac tech. im talking "Tons" and operating pressure.

    when i am talking to a reefer tech. im talking HP. and coils temperature.
















    which language does heat transfer professionals talk??





    Don't interrupt me while i'm talking to myself

  2. #15
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Post Likes
    I'm full a time "Market Man" and I'm dumb as hell.

    I'm a likin' this thread though

  3. #16
    Join Date
    Apr 2005
    Location
    Oregon
    Posts
    13
    Post Likes
    In general there is a rule of thumb that can be applied when nothing but horsepower is known.

    1 hp at a/c temp is around 1 ton or 1:1
    1 hp at med temp is around 2/3 ton or .66:1
    1 hp at low temp is around 1/3 ton or .33:1

    This is really general but can get you pretty close when no other info is available. (destroyed or unreadable tags are the norm) Or when someone forgets to tag the orifice size that's inside of a tx valve.

  4. #17
    Join Date
    Mar 2005
    Location
    N.J.
    Posts
    448
    Post Likes
    Heat Transfer Professionals ....I just found the name for my new company !!!!Thanks !!!!H. T. P. May I help You.... What do you think??? ... Any way...I found the information in this thred very helpful and quite interesting however it brings up a question. How or should you also factor in the refrigerant type and its specific heat value in to the equation when figuring compressor capacity of heat transfer at certain saturated condtions?

  5. #18
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes
    Originally posted by richper
    Heat Transfer Professionals ....I just found the name for my new company !!!!Thanks !!!!H. T. P. May I help You.... What do you think??? ... Any way...I found the information in this thred very helpful and quite interesting however it brings up a question. How or should you also factor in the refrigerant type and its specific heat value in to the equation when figuring compressor capacity of heat transfer at certain saturated condtions?

    By ploting the particular system on a PH or Mollier diagram for that particular refrigerant.


  6. #19
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes

    so what is

    the right answer?

  7. #20
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes

    Re: so what is

    Originally posted by air2spare
    the right answer?
    evaporator and condensor conditions determine the horse power need to provide a ton of refrigeration from a given compressor...

    what was the question?

  8. #21
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    Post Likes
    12,000 btuh = 1 ton
    no HP relationship to btuh

    CF12K6E-TF5
    130 Condensing
    -20 Evap 7070 btuh
    -10 Evap 10200 btuh
    -5 Evap 12000 btuh (nominal rating)
    0 Evap 13900 btuh

    110 Condensing
    -20 Evap 10700 btuh
    -10 Evap 14800 btuh
    -5 Evap 17100 btuh
    0 Evap 19700 btuh

    different for other cond and evap temps, where are you at ?

    get a performance sheet from Copeland Wholesaler to
    see ratings at other conditions

    Sorry, you cannot relate HP to ton or btuh
    (never was true, that was an old wife's tale)

  9. #22
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    rocket is correct. It is all about volumetric efficiency. The higher the head pressure and the lower the suction pressure, the lower the cooling capacity (tons) at the same HP.

    Actually, as the head pressure increases and the suction pressure decreases the BHP increases while the capacity decreases.


  10. #23
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes

    Im done

    Originally posted by NormChris


    rocket is correct. It is all about volumetric efficiency. The higher the head pressure and the lower the suction pressure, the lower the cooling capacity (tons) at the same HP.

    Actually, as the head pressure increases and the suction pressure decreases the BHP increases while the capacity decreases.


    (^%$%$*&*&%#@%%&_()*(*%^%#@#%^^%**)
    over and out

  11. #24
    Join Date
    Sep 2004
    Posts
    159
    Post Likes
    [QUOTE]Originally posted by gerryboy00
    [B]when i am talking to a hvac tech. im talking "Tons" and operating pressure.

    when i am talking to a reefer tech. im talking HP. and coils temperature.

    which language does heat transfer professionals talk??



    It depends on what the professional is doing. If he talking about capacity, then its usually tons or btuh. If he needs to match a motor to an open drive compressor, then its horsepower. If its a comparison of efficiency/cycles, then it could be bhp/ton. It is rare that a proffessional would ever interchange one for the other unless done in purely thermodynamic terms where there is a direct conversion of btuh to hp and visa-versa.

  12. #25
    Join Date
    Dec 2004
    Location
    Sunny So Cal!
    Posts
    649
    Post Likes
    who's got time to sit and chat w the A/C guys at a parts house? I only notice them when its a demo day and they've eaten all the carne asada....and yesterdays donuts too....
    OK, so whats a little "home by 7 pm" envy eh?

  13. #26
    Join Date
    Dec 2003
    Posts
    1,117
    Post Likes
    The way I have always known it is according to the application (Low, Med, High) the electric motor in the compressor is the determining factor for hp, For example:

    4000 btu's at -10* evap 120 cond (Low temp)needs a 1hp motor(1hp compressor)to run efficiently at these conditions with the correct designed displacement.

    8000 btu's at +20* evap 130 cond needs a 1hp motor (1hp compressor)to run efficiently at these conditions with the correct designed displacement.

    12000 btu's at +45* evap 130 cond needs a 1hp motor (1hp compressor)to run efficiently at these conditions with the correct designed displacement.

    12000 btu's is and will always be "One Ton" of cooling no matter the application.