    I'm working in a Copeland compressor, model CF12K6E-TF5, and want to know how many horse power of capacity is, the name plate don't say anithing about it.

    Accord with Copeland handbook, compressor nominal capacity in this case is 12000 (I assume are BTU's). If this is correct, compressor capacity would be One ton.

    But, what is the relationship between BTU's and horse power?. A friend says that when a compressor capacity is specified just in BTU's, the relation is one to one, that mean one ton equal one HP, is that correct?.

    Thanks.

  2. #2
    Join Date
    Jan 2005
    Posts
    38
    Post Likes

    there are..

    ...two ways to measure HP,mechanically(work) or electrically(watts)

    1000w (1 kw)= 1.34 hp

  3. #3
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    The capacity of a compressor is not a fixed number such as one hp per ton. The capacity varies depending upon the suction pressure and discharge pressure.

    As the suction pressure decreases or the high side pressure increases, the capacity drops. Raising the suction pressure and lowering the discharge pressure increases the capacity for the same hp compressor.

    It so happens that a typical air conditioning compressor with a one hp motor will provide one ton of cooling capacity at "normal" air conditioning operating pressures. This is an approximate "rule of thumb" conversion. If the high side pressure is abnormally high or the system is operating on a hot day, the one hp compressor will provide less than one ton of cooling. If the suction pressure is abnormally low the same one hp compressor will again operate at a lower capacity.

    A low temperature system operating with the required lower suction pressure necessary to achieve the lower suction temperature will require 2, 3, 4, or even 5 hp to obtain one ton of cooling capacity.

    This is all related to the changing volumetric efficiency of the compressor. Volumetric efficiency is another topic and an interesting one at that.

    Norm

  4. #4
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    Compressors do not have their capacity listed on them because the actual capacity will depend upon the pressures. Each compressor model has a chart or graph published by the compressor manufacturer where you can find the actual operating capacity of the compressor if you know the suction and discharge pressures. The charts usually provide the actual power consumption for different operating pressures as well.

    Norm

  5. #5
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    According to that over-hyped text book,
    1btu/h=.000393hp.
    Therefore a one ton compressor requires 4.7hp.

    (12000 x .000393 = 4.716hp)

    But which is "nominal",the btu/h or the hp?

  6. #6
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes
    Originally posted by jacob perkins
    According to that over-hyped text book,
    1btu/h=.000393hp.
    Therefore a one ton compressor requires 4.7hp.

    (12000 x .000393 = 4.716hp)

    But which is "nominal",the btu/h or the hp?
    Jacob, this is totally untrue. Reread my previous posts on this thread. There is no fixed relationship between hp and btuh!

    Norm

  7. #7
    Join Date
    Feb 2003
    Location
    NH & Cebu
    Posts
    1,611
    Post Likes
    Guys that do strictly A/C refer to compressors in tonnage...."it was a 5 ton compressor"

    reefer guys...being the more intelligent breed...refer to compressor size in horsepower...."it was a 20HP compressor"

    A/C guys know nothing about the relationship between HP and tonnage and evap temp


    There...how's that for opening up a can of worms?

  8. #8
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    Post Likes
    the CS12 has a btuh range of 3330 to 25700
    pretty wide huh ?
    depending on refrig, application, suction, condensing
    all compressors will have varying btuh curves

    the primary factor in compressor design is
    bore, stroke and cfh, not horsepower

    what A/C guys call a 5 ton compressor is also
    used in as 2 ton cooler, 7-1/2 ton A/C,etc.
    get the idea

    if you want to relate btuh to hp then relagate
    yourself to the status as parts changer

    note: all current 5 ton A/C units do not have a
    5 ton compressor (4 or 4-1/2 usually used)

  9. #9
    Join Date
    Apr 2005
    Location
    Knoxville,TN
    Posts
    15
    Post Likes
    Most of the time if you compare HP to tons of refrigeration
    You would have to look at the btu capacity on a +45F evap. (common A/C evap temp)
    For example:
    F3AD-A201 Copeland 2HP condensing unit R22 has a BTU capacity of 23,600 @ +45F evap temp. (right at 2 tons)But on a +25F evap it will only handle 16,200 btu. So it can be relative but not always.
    Just another way of looking at things.

  10. #10
    Join Date
    Sep 2004
    Posts
    159
    Post Likes
    Thermodynamically the HP required can be calced by:

    Mass flow(lbs/hr)x heat of compression (btu/lb) x 2545 btu-hr/HP. All of this at a given set of specific conditions.

    To get total hp, you would have to account for friction inside the compressor, which isn't something that can be calculated.

    Add the thermodynamic Hp required to the friction requirements and thats the total.

    It is interesting to only calculate the thermodynamic work required for a given refrigerant and set of conditions, and then compare it to the same refrigerant operating at different conditions. You will see that as conditions change, the HP required also changes; it isn't a constant number.



  11. #11
    Join Date
    Aug 2003
    Posts
    1,311
    Post Likes
    "hvacmd2002" change your screen name before implying that a/c guys don't know about hp/tonnage relationship, or the basic lack there of. there is no direct relationship it is as Norm says.

    disclaimer; yes it is a joke, no i was not trying to imply that you did'nt know the difference.


    [Edited by hvac3901 on 04-27-2005 at 02:03 PM]

  12. #12
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Post Likes
    Originally posted by hvacmd2002
    Guys that do strictly A/C refer to compressors in tonnage...."it was a 5 ton compressor"

    reefer guys...being the more intelligent breed...refer to compressor size in horsepower...."it was a 20HP compressor"

    A/C guys know nothing about the relationship between HP and tonnage and evap temp


    There...how's that for opening up a can of worms?
    And heat transfer professionals think that this type of irrational, generalized reference to HVAC vs. Refrigeration is silly.

    Heat transfer professionals refer to the compressor by make, model, serial, capacity at a given evap temp, and, often CFM, kW, EER and Mass Flow.


  13. #13
    Join Date
    Feb 2003
    Location
    NH & Cebu
    Posts
    1,611
    Post Likes
    Originally posted by condenseddave
    [
    Heat transfer professionals refer to the compressor by make, model, serial, capacity at a given evap temp, and, often CFM, kW, EER and Mass Flow.

    [/B]
    Wait. So, if I'm working on a rack, and point to compressor 2, I have to tell you all THAT? Or can I just call it the 10HP?

    Heat transfer professional. I've never heard that term before. Is there a secret handshake that goes with that?

    But seriously, have you ever heard an A/C guy refer to a compressor in anything but tons? Now I'm sure that the A/C guys in here are a cut above. But ask 10 guys at the supply house about tons and HP and evap temp. 9 won't have a clue.