    I have two Trane, cooling, non-bleed, single direction flow TXV valves:

    Valve A is a TAYTXVA0E3C designed for 3 to 3.5 ton AC units

    Valve B is a TAYTXVA0H3C designed for 5 to 6 ton AC units

    Both valves have a 3/8 liquid line feed.

    Question: I place the temperature sensor bulb of both valves in warm water so each valve is WIDE open. Each valve is being supplied with liquid R-22 from their respective design condensers at the same pressure.

    Which valve will allow more R-22 to flow and why?


  2. #2
    Join Date
    Jun 2004
    Location
    Maryland's Eastern Shore
    Posts
    892
    TAYTXVA0H3C

  3. #3
    Join Date
    Feb 2005
    Posts
    27
    The H3C will allow more flow.

    Why: Because its set up for a larger tonnage unit. If you put E3C TXV on the 5 ton coil you starve the evap.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,165
    So what are the symtoms, that your testing the valves.
    Contractor locator map

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Dec 2004
    Posts
    441
    Originally posted by wendel
    I have two Trane, cooling, non-bleed, single direction flow TXV valves:

    Valve A is a TAYTXVA0E3C designed for 3 to 3.5 ton AC units

    Valve B is a TAYTXVA0H3C designed for 5 to 6 ton AC units

    Both valves have a 3/8 liquid line feed.

    Question: I place the temperature sensor bulb of both valves in warm water so each valve is WIDE open. Each valve is being supplied with liquid R-22 from their respective design condensers at the same pressure.

    Which valve will allow more R-22 to flow and why?

    Valve B. Why? 5Ton vs.3Ton! We need to have a serious talk here about boiling and condensing.