Hi everyone,
2 months ago, we had the HVAC professional to replace the contactors on our heat pump system. Now i have the same problem again, the contactors aren't triggered on when heating is on. And, he told us that we need to replace another part in the system. I found on the web that the part he wants to replace called adjustable temperature same as on the pic, web link below. Part # AT012.
http://www.alpha2omegaparts.com/appl...rmostats.shtml
So he left me with a wire with two clamps at the ends to bypass this when the contactors aren't triggered. I did what he told me and it worked.
my question is what is this adjustabel temperature for?
Thank you in advance.
-
02-04-2005, 07:35 PM #2
The first thing is to call another contractor because this one is going to kill you.
The control you are refering to is a tempature saftey. The picture you posted is not an OEM part. You should replace the equipment if OEM part is not manfactured anymore.
I only use this part in an emergancy situation, or on a non-critical system (I have used them to turn fan on when used with a wood stove). In this situation if it fails it's not a big deal.Karst means cave. So, I search for caves.
-
02-05-2005, 04:21 AM #3
Professional Member
- Join Date
- Apr 2003
- Location
- Iowa
- Posts
- 749
as I scratch my head on this one. WHATTTTTTTTT???
get a second opinion...
-
02-06-2005, 01:12 AM #4
Professional Member
- Join Date
- Apr 2003
- Location
- arizona
- Posts
- 629
this guy will be in jail when you hook the clamps to the wrong connection and kill yourself.. find a new legitimate contractor not BOZO good luck
-
02-06-2005, 04:23 AM #5
Member
- Join Date
- Jan 2005
- Posts
- 63
it doesnt take a qualified contractor to know that !
That you just dont by-pass a safety in any situation, or jumper anything out! however, Do call a qualified contractor or qualified tech/mechanic!
-
02-06-2005, 08:05 AM #6
An adjustable limit, they are common, so why didn't he get you one right away, its a safety device to keep your unit from melt down.
If its tripping, some thing else is wrong, thats just a symtom.
You might want another contractor to find the real problem with your unit.