    We recently replaced an old boiler with a new Buderus oil fired boiler-----new t-stats,pumps,controls.
    Customer calls today ---the t-stat is set for 65 and the room is up to 80+ degrees. Checked pumps --not running,contacts not stuck closed,boiler not running. Hummmmm--boss says its migration of water.
    Anybody ever run into something like this????????

  2. #2
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,856
    It is called a gravity system.(I think)

    Install a zone valve or check valve.

    I have opened the check valve on a system that had a bad circ. and none in stock. It would heat the house just fine.
    Karst means cave. So, I search for caves.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,167
    Forgot to install the flo chek, left it turned open, or dirt got in it.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?