Thread: York 80% efieciency furnace , going crazy

  1. #1
    heatseeker Guest

    Question

    I have been working on a york furnace that is acting crazy ,the board says it is locking out because of a roll out switch. all rollout and pressure switches check out good (24 volts etc). The unit has manual reset switches on it and all of them right. This thing will run right, heat up and shut off then , house cools down and it will call for heat but no ignition, ignitor glows sometimes,sometimes it doesn't, sometimes it glows twice but the gas valve won't open. turn it off for awhile then turn it back on and it will warm up the house and act up again. board always flashes roll out switch open.

    [Edited by heatseeker on 02-01-2005 at 08:20 PM]

  2. #2
    Join Date
    Feb 2004
    Posts
    2,597
    Post Likes
    you're losing voltage somewhere. trace it.

  3. #3
    Join Date
    Apr 2003
    Location
    Iowa
    Posts
    772
    Post Likes
    look for bad connections, board could be bad..... rollout switches are ok? limit is not opening?

  4. #4
    Join Date
    Jan 2005
    Location
    Gilroy, Calif
    Posts
    188
    Post Likes
    put jumpers on roll out sw and run a cycle. I know this may sound stupid but the flame shield is in place, right?

    [Edited by gje1 on 02-03-2005 at 10:14 PM]

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •