Page 2 of 2 FirstFirst 12
Results 14 to 15 of 15

Thread: Correct sizing

  1. #14
    Join Date
    Jul 2004
    Post Likes
    Originally posted by martik

    The energy test report says it was originally 10.85 ACH @50Pa which was equal to approx a 468 sq inch hole.
    After the upgrades it went down to 4.5 [/B]
    Never mind. Sounds like you had a blower door test. Tight houses can get well under 1 ACH, but that's without a blower forcing air out.

  2. #15
    Join Date
    Feb 2005
    Post Likes
    If 30,000 btus is correct,and you get the closet size to it,the cfms reqired ,for each room ,will not exceed the cfms of that unit,period.

    More cfms will only be required if you need more btus.

    Your ducts are larger than needed,so with VS fan no problem.Standard fan ,you may need a damper in the main trunk to raise the static,to keep the cfm down,so you get a proper temperature rise.

    Main thing is to be sure the load calculation is correct,sounds like it could be.

    Good idea to calculate the cooling and get a furnace that can handle the tonnage ,if someone ever wants to add cooling.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365