    I do the hvac in a building with a honeywell control system. There are around 100 vav and fan powered boxes that are connected on a lon network and there is a lon interface connected to the honeywell system. The rest of the honeywell system is not lon according to the honeywell guy, the controllers for the air handlers are xl 50 I think. The honeywell system seems to only monitor the boxes but we cannot actuate the valves from the computer. Can I access the vav boxes with lonspec and how do they mix the two systems.

  2. #2
    Join Date
    May 2002
    Posts
    9,564
    See that plug-in communication module on the Excel 50? - That can be E just as easily as C. (just swap it out for LON)

    If it were me I'd change the 50's to E and run the whole thing through a LNS platform.

    No tiered software issues.

    Otherwise, you need CARE and Evision or just the latest CARE.