  1. #40
    Join Date
    Sep 2010
    Location
    Madison WI
    Posts
    77
    After 18 months who had to trash all that ice cream or did they sell the frozen product as new might look at fed reg on the food

  2. #41
    Join Date
    Dec 2007
    Location
    houston, texas
    Posts
    3,787
    [quote=jpsmith1cm;858382

    Not to be a jerk, mccool, but how would low airflow contribute to this problem.[/quote]

    Looks like he had it right
    I'm not tolerating Political Correctness anymore, from now on it's tell it like it is.

    Veto Pro Pak - The best tool bag you'll ever own






  3. #42
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,687
    Quote Originally Posted by Texas-Tech View Post
    Looks like he had it right
    No. he did not.

    The problem WAS airflow related, but the case had 3 times the airflow that was required, not low airflow as he suggested.

  4. #43
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,687
    Quote Originally Posted by Herb1025 View Post
    After 18 months who had to trash all that ice cream or did they sell the frozen product as new might look at fed reg on the food
    For most of the year, they run this case as a medium temp case. In that mode, it holds reasonably well.

    There has been no product loss.

  5. #44
    Join Date
    Sep 2010
    Location
    Madison WI
    Posts
    77
    we used to have to check each case temp and rack pressures now we go on the computer and look at every thing That control system even calls your cell or computer if something is not right. Nice to set coil td and not have to take gages or temp probe out of the truck. The new controls will not brake the bank no more frozen food case full of product that the juice is liquid.

  6. #45
    Join Date
    Oct 2009
    Location
    310
    Posts
    115
    Quote Originally Posted by jpsmith1cm View Post
    Hopefully the picture I took of the DRSA is adequate to provide all refrigerant side data.

    Problem is this:

    Dual temp single deck case would NOT hold temp in LT mode. Did a 'fair' job in MT.

    Tech#1 was out and condemned the powerhead and when that did nothing, replaced the whole TXV. When THAT didn't work, I was called in.

    Cut in a pressure tap and SG on the liquid line to confirm quality of liquid and the pic I posted gives the results. Sightglass was perfectly solid.


    So. Fire away.
    So, what's the low end temperature of the suction line where the sensing bulb of the powerhead is located? Maybe the superheat is off.

  7. #46
    Join Date
    Oct 2009
    Location
    310
    Posts
    115
    Quote Originally Posted by jpsmith1cm View Post
    TXV was wide open at the time this picture was taken.

    All heating vents were already checked and aimed away from this case. (Yes, it is an open air single-deck type case)

    Not to be a jerk, mccool, but how would low airflow contribute to this problem?


    Ok. Time for another hint. It hasn't worked right in a very long time if it ever worked right. Our company didn't install it, but we got saddled with the repairs.
    *Keep in mind that I'm reading as I post..

    Hmmm... Maybe not all the components aren't manufacturers and has been retrofitted?

  8. #47
    Join Date
    Oct 2009
    Location
    310
    Posts
    115
    Quote Originally Posted by KB Cool View Post
    Wow!!! who would have thought too much air flow on a refer case. I usually just check to see if the coils frozen, motor is working and spinning the right way. Nice find though and glad you shared it with us. I'll have to keep it in mind. May need it someday.
    Same here!

  9. #48
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,647
    I think there are still questions.

    1) Does the customer switch the unit from MT to LT for Seasonal promotions, such as turkeys for Thanksgiving?

    2) The other guys you inherited the store from... are they reputable?

    The reason for both these questions why / how did the wrong fans get in there? Was it an oopsdammit (guys just stocking & selling 9wt motors) or were they trying to beat a different problem?

    It's been several months now, should be warm & humid there, how's that system running now?

    Nice find either way. Not sure I would have used anything more accurate than the back of my hand to check airflow.
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  10. #49
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,687
    Engineerdave,

    Yes, the store has the ability to switch from med to low at will with a key switch. They only do so for a week at the holidays, though. To date, no more complaints on the case.


    As far as the motors are concerned, this particular manufacturer (who has reps on this site so I'm not naming names) uses a unitary motor design. Basket, motor and blade are one large assembly. Can't remove the blade, so you aren't likely to swap in the wrong part. The parts in place were OEM, so you do the math.


    Oh, yeah, due to the age of the case, the manufacturer went back on the verbal agreement to send me new motors and the operation of the system remains unchanged as the customer has also refused to pay for the parts.


    As far as the company we inherited this mess from......... I love taking over their accounts. They always lead to good, educational problems like this.

  11. #50
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    I learned a lot from this thread. There is a company that keeps coming to the market I work at selling "energy rebates" for refrigeration. We've actually done quite a bit of business with them--got a bunch of LEDs installed in glass door cases, floating head pressure controls, etc. for great price--but now they want me to buy and install ECM motors for all of our cases and walk ins. Keep in mind these guys are NOT refrieration mechanics and can be kind of pushy salespeople. So I was like, "uhh, guys...I think these fans need to be spec'd just right for the cases. Like, CFM and the like?" They just dismissed me. I was like, well, can you supply me with data that the rpms of the motors will be exactly the same? They couldn't, so I scrapped the program.

  12. #51
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,687
    Iceneck,

    To hijack my own thread, I think you are wise to stay clear of ECMs in MOST refrigeration applications.

    One plugged drain and all that fancy, EXPENSIVE technology goes right down the drain, so to speak......

    I've 'retrofitting' ECMs with 9w and other appropriate sized motors for years.


  13. #52
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Quote Originally Posted by jpsmith1cm View Post
    Iceneck,

    To hijack my own thread, I think you are wise to stay clear of ECMs in MOST refrigeration applications.

    One plugged drain and all that fancy, EXPENSIVE technology goes right down the drain, so to speak......

    I've 'retrofitting' ECMs with 9w and other appropriate sized motors for years.

    Jps,

    Didn't mean to hijack your thread...I thought it was along the same lines as the problem you posted, though.

    As far as what you said about ECMs, EVERY tech and EVERY salesperson at the supply houses have told me the same thing you did.

    Thanks again...

Page 4 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event