Results 1 to 5 of 5

Thread: Rheem heat pump

  1. #1
    Join Date
    Sep 2003
    Posts
    17
    Post Likes
    So I can read most model numbers, but the Ruud/Rheem numbers continue to baffle me. What is a Rheem model RBHA-14J05NFAA?
    And on a 52 degree day, is a 10 differential with 80 degrees at the closest register in heat pump mode satisfactory?
    Thanks, JLMathis

  2. #2
    Join Date
    Nov 2001
    Posts
    1,874
    Post Likes
    what is 10 differential ?
    Are you talking temp rise ?
    If so how are you measuring it, and where from ?
    On a 52* day you should do much better then 80* at the closest suppy.
    Even the longest one should be much higher then that.
    Check your filter and check for air leaks.
    If you try to fail, and succeed.
    Which have you done ?



  3. #3
    Join Date
    Jul 2003
    Location
    Central Florida
    Posts
    95
    Post Likes
    That is a 1 1/2 or 2 ton with 5KW electric heat. 10º seems pretty light....is the heat pump condenser running?

  4. #4
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,854
    Post Likes
    Go here page three

    http://www.rheemote.net/docstore/web...1_509_Rev8.pdf

    You will need adobe acrobat.

    This site is restricted but some info is not.
    Karst means cave. So, I search for caves.

  5. #5
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    39,006
    Post Likes
    You need to measure temp rise right over the unit, not at registers. On a 52 degree day with just the heat pump, you should be around 30 degree increase. 5kw isn't much heat so air won't be too much warmer with backup on.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.