The area of the control that tells you how many RPM that the motors are running, is not really a place you should be going. I know it is your stat and system, but you could accidentally make some changes there that could adversely affect the operation of the system.
That being said, are these alarms current or are you just seeing them in the history?
Code 12 simply means that there was a call for heat when the power was turned on to the furnace. It is not a fault code, but a information code.
Code 32 and 43 refer to the low stage pressure switch, and could be totally normal. The inducer motor will run at the slowest rpm possible and still make the pressure switch. That is why it is normal for it to be changing rpm (among other reasons). It has to first find that speed, so during it's learning curve it is nomal for the switch to open.
If these are codes in history, forget it, all is well. If they are reoccuring, you need to call the installer to check them out. Could be any number of reasons for them, all of which you really need someone with experience to find.
If all else fails....Try reading the directions!