Results 1 to 4 of 4

Thread: duct sizing

  1. #1
    Join Date
    Jan 2005
    Posts
    2
    Post Likes
    Does the size of the unit call for different sizes in the ductwork when the unit size increases/decreases by around 2 tons or so?

  2. #2
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,417
    Post Likes
    99.9999% of the time yes.

    There is the odd chance that the original duct installed was way too big and will work fine with the larger system, but thats very very rare.

    Only way to know is have someone who knows thier stuff do a load calc on your house, then check out the duct to make sure it's sized properly (either using old or putting in new).

  3. #3
    Join Date
    Dec 2003
    Posts
    1,195
    Post Likes
    Most definitely, assuming they were right to start with. Run a Manual D and see where you stand.
    "That's good enough..." usually isn't.

  4. #4
    Join Date
    Nov 2004
    Location
    Naples, Fla.
    Posts
    1,403
    Post Likes
    Yes size does matter. (makes you want to snicker does'nt it)

    Ask your contractor if he owns a ductalator, in fact 2 ductalators - 1 for ridged, one for flex.

    90% of all products are designed for a max static pressure of .5" WC. If you exceed the max - you'll have a host of undesireable side effects IE:

    Noise, Evap. H2O blowoff, premature compressor failure, premature HX failure, loss of effiecancy, poor heat, poor cool, voided warranty, just to name a few.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event