Results 1 to 5 of 5
-
01-31-2005, 12:32 PM #1
Regular Guest
- Join Date
- Jan 2005
- Posts
- 2
I have a newlu installed Trane xv90 with a VisionPro 8320. This was a floor model with a 2002 manufacture date. Installed yesterday and all was fine. This morning blower was running but no heat. Red LED blinking twice indicating a system lockout. I reset and started up again, the ignitor fires the burners and then the burner immediately shuts off. I checked both vents and all is clear. Any ideas?
-
01-31-2005, 12:54 PM #2
Professional Member-T-bad email, rejected
- Join Date
- Feb 2004
- Location
- Tucson AZ
- Posts
- 55
I am not familiar with thus model but this problem is typical of the ignition control not sensing the flame. There is typically a flame sensing rod that will have a small dc micro amp current when a flame is present. Check that all electric connections are good and that the flame sensing rod is clean. You can clean with steel wool. This is just a place to start you will need specifications and a multi-meter that is able to measure dc micro amps to go any further.
-
01-31-2005, 02:59 PM #3
Call the installer back!
DO NOT even mess with it...How tall are you Private???!!!!
-
01-31-2005, 03:42 PM #4
bob...this is not a d-i-y site. call back your contractor.
FILL OUT YOUR PROFILE!!
-
02-01-2005, 10:50 AM #5
Professional Member-T-bad email, rejected
- Join Date
- Feb 2004
- Location
- Tucson AZ
- Posts
- 55
sorry tinner
I apologize for the d-i-y info. I misread Willies post. Thought he had installed the furnace. I agree you should call back the installing contractor. It should be under warranty if recently installed.


Reply With Quote