    I have a newlu installed Trane xv90 with a VisionPro 8320. This was a floor model with a 2002 manufacture date. Installed yesterday and all was fine. This morning blower was running but no heat. Red LED blinking twice indicating a system lockout. I reset and started up again, the ignitor fires the burners and then the burner immediately shuts off. I checked both vents and all is clear. Any ideas?
    Tucson AZ
    I am not familiar with thus model but this problem is typical of the ignition control not sensing the flame. There is typically a flame sensing rod that will have a small dc micro amp current when a flame is present. Check that all electric connections are good and that the flame sensing rod is clean. You can clean with steel wool. This is just a place to start you will need specifications and a multi-meter that is able to measure dc micro amps to go any further.
    Jul 2002
    Zelienople, Pa
    Call the installer back!
    DO NOT even mess with it...
    chicago suburbs
    bob...this is not a d-i-y site. call back your contractor.
    FILL OUT YOUR PROFILE!!
    Tucson AZ
    sorry tinner
    I apologize for the d-i-y info. I misread Willie’s post. Thought he had installed the furnace. I agree you should call back the installing contractor. It should be under warranty if recently installed.