    Our condo is currently AC and Heat with GE Zoneline. We have approxiamately 9 units. They are noisy and have to be concealed with window seats between each one. Is there any other choice for us? Please help.

  2. #2
    Join Date
    Nov 2002
    Location
    emerald city, sc
    Posts
    1,469
    is there anywhere to run duct work ?
    you say it's a condo, make sure regulations don't prohit the installation of outdoor units.
    ductless mini splits are available if no where to un duct work. they are not cheap though.
    i wanted to put a picture here

  3. #3
    Join Date
    Jan 2005
    Posts
    3

    Zoneline, Any choices.

    Our units are inside the building. We cannot run duct work in the ceiling. We could run vent around the walls that would show.

    We also do not have anygas available in this building.

    Thank you for your help.

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,599
    The new GE 5500 is so much quieter than most of these beasts. As far as I know, it's the only one that will run the heat pump with backup on so should be the cheapest to run too. 9 of them, wow!

  5. #5
    Join Date
    Jan 2005
    Posts
    3
    Thank you for your suggestion. I gather using the Zoneline is our only option. I will look into the 5500.