    I've got a Taco 007 circulator on a SlantFin gas-fired boiler, 145,000BTE D.O.E, 125,000BTU for water. Furnace is not doing potable hot-water. Unit installed mid-1999.

    If it runs for 20 mins straight, I swear the circulator gets hotter than the water-output of the furnice (which is 180degrees)

    Does its temp. indicate a problem?

  2. #2
    Join Date
    Jan 2005
    Posts
    56
    Post Likes
    You might want to check the actual temp at the circulator. Does it have a well you can insert a thermometer into? You could also read the temp with a digital probe against the surface of the circulator. What is the temp in and out?

  3. #3
    Join Date
    Feb 2004
    Posts
    2,597
    Post Likes
    if the amp draw is within specs., don't worry about it.


  4. #4
    Join Date
    Jan 2005
    Posts
    10
    Post Likes

    hot circulator

    Is that a wet rotor type circulator ?
    Is the circulator motor in the horizontal position?

  5. #5
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Post Likes

    Re: hot circulator

    Originally posted by bestexpert
    Is that a wet rotor type circulator ?
    Is the circulator motor in the horizontal position?
    Taco "00" series are all wet rotor.

  6. #6
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    Taco "00" pumps are wet rotor and get extremely hot to the touch. Hard to believe they can work in that environment. Most of these pumps are piped directly off the header of the boiler nowadays, where water temps exceed 220F and the pumps are working well.


  7. #7
    Join Date
    Nov 2001
    Location
    Moose Jaw, Saskatchewan, Canada Occupation:Interprovincial Plumber, Commercial Gasfitter Interests:
    Posts
    2,415
    Post Likes
    The 0014 can be mounted vertical if the psi is over 20. Go figure.
    I love my job, but paydays Thursday

  8. #8
    Join Date
    Mar 2001
    Posts
    365
    Post Likes

    Vertical

    Your right.......The 00's can run vertical if you boost up the pressure above 20# if pressure drops below 20# they make noise... I always ask "Why?" Why bother ? Install them hozontal and live in peace....See no reason

  9. #9
    Join Date
    Oct 2001
    Posts
    2,118
    Post Likes
    Few days ago a circulator in my house quit. It is Taco 007. I took it apart, and found seized rotor. In the past I moved it from original position on return, to discharge line after air scoop. I mounted it in vertical position with impeller facing up. Will never do this again. Now I turned pump flanges 90 degrees and rotor is horizontal like it was originally.
    After I freed rotor under running facet I noticed one thing.
    When holding cartridge horizontally, rotor moves more freely then in vertical position,
    almost like it would need a trust bearing to work right.
    There is one thing that makes me wander.
    Why increasing pressure above 20psi makes a difference?


    [Edited by sigma on 03-02-2005 at 12:09 AM]

  10. #10
    Join Date
    Jan 2005
    Posts
    99
    Post Likes
    If I remember correctly, which may be questionable, most packaged boiler systems in the past would send there boilers with 00 preassembled in the vertical position, I cant say that Ive seen premature failure due to this.Never heard of boosting psi to accomodate circulator. Interesting. This may not be a popular view, but 3-piece pumps when maintaned properly perform more reliably than wet rotors. The curves just a little to flat for my taste, not quite as versatile. I wouldnt be to concerned about the heat, they do run hot.

  11. #11
    Join Date
    Aug 2002
    Posts
    391
    Post Likes

    Wink

    Why do people call a boiler a furnace? ( Just bugs me) Your other posting was about gurgling water in the base board, you may have air in the loop and the circulator is running at high temp limit.
    The obvious is obvious

  12. #12
    Join Date
    Jan 2005
    Posts
    99
    Post Likes
    Thats a possibility, how hot is hot. Can you strap a temp gauge to the pump? Still hearing gurgling?