Page 1 of 2 12 LastLast
Results 1 to 13 of 17

Thread: trane heat pump

  1. #1
    Join Date
    Jan 2005
    Posts
    17
    Post Likes
    could someone please tell me if when its gets cold enough for the heat strips to come on is the heat pump unit outside suppose to be running? i was told it is not suppose to be running they said it would create a double electric bill which i have thank you. i was told only the fan upstairs is suppose to be running to push the heat strip heat out.

  2. #2
    Join Date
    Oct 2004
    Posts
    1,722
    Post Likes
    The heat strips should come on to assist the heat pump or be used for emergency heat, when the heat pump has failed.
    Get back to work.™

  3. #3
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    heatpump runs allthe time except in defrost mode.
    heat strips should be wired where half of the strips are used for auxillary and all for emergency heat.
    auxillary strips come on when temp is 1 or 2 degrees below setpoint.

  4. #4
    Join Date
    Feb 2004
    Location
    cocoa fl
    Posts
    143
    Post Likes

    Lightbulb

    the double electric bill is all in you're head...

  5. #5
    Join Date
    Feb 2004
    Location
    cocoa fl
    Posts
    143
    Post Likes

    Lightbulb

    did you think when it is cold enough for the heat strips to come on that the heat pump will go off leaving the heat strip to heat the house by it's self ? won't happen the heat pump can pull heat out of the air is very low temps but it does have to defrost ann will need help in freezing temps to heat a house.. but you'll have to find a better excuse or another person to blame you're high heat bill on.. i have a gripe why do uninformed homeowners come on here looking to dump there problem on the havc tech or installer when they have no idea how the equipment operates.homeowners before you blame get and idea of what else it could be it's not always are faults. now look at other things that could cause a high electric bill thank you

  6. #6
    Join Date
    Jan 2005
    Posts
    17
    Post Likes
    Thread Starter
    the doulble bill is not in my head i can tell you. i have a 275.00 electric bill and its not from anything else except for this lousy heat pump. i have a 1332 square foot house and live in south carolina and my house is cold as heck but thank you anyway. i was not trying to find a excuse just a solution and i thought that is why i signed on to this page. sorry for your trouble!!!!!!!!!!!

  7. #7
    Join Date
    Feb 2004
    Location
    cocoa fl
    Posts
    143
    Post Likes
    well how about this for a solution call a tech ??????

  8. #8
    Join Date
    Jan 2005
    Posts
    17
    Post Likes
    Thread Starter
    wow you were so helpful i want to thank you so much for your help matt!!!!!!!!!!!!!!!!

  9. #9
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    It is possible that you have a problem with your heat pump that is causing the system to run the electric heat to much, wich would drive your bill up.

    You should get the system checked out by a pro.

  10. #10
    Join Date
    Dec 2004
    Location
    Derby City
    Posts
    4,120
    Post Likes
    Heat Pump 101: Heat pump will be sized to satisfy the COOLING requirements. The manufacturer will provide information on the heating available with this PROPERLY SIZED heat pump system. Heat pump will satisfy heating requirements to the balance point (lower with higher efficiency equipment) but usually around high 20's or low 30's. At that point, the heat pump will continue to operate and the resistance heat (strip heaters) will come on as needed to supplement the heat pump. This is accomplished with sequencers that bring the strip heat on incrementally. for example, if you have 15 KW of aux. heat it may come on in 5 kw 10 kw steps. Even at 0 or below outdoor temp. the heat pump contributes significantly toward the heat load. Remember that the whole concept of a heat pump is that it is less expensive to MOVE heat from point a to point b than to generate the heat. I believe that the resistance heat (heat strips) should be sized to carry the load, or as much as possible, on their own, so that if emergency heat is required, it can provide adequate heat. Even under these circumstances, the heaters should come on in steps. Newer heat pumps are much more efficient that the "first generation" units. And in some areas, can be MORE efficient that other fuels, i.e. lp gas, oil, etc. As indicated early on, and so that I am consistent in what I say, DO CALL A PROFESSIONAL. I don't believe it was centralflinstaller's intent to be sarcastic, but the bottom line is to call in a professional to diagnose the exact problem and correct it. There is not much you can do as a HO to correctly and SAFELY troubleshoot the system.

  11. #11
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Post Likes
    Originally posted by summer1961
    could someone please tell me if when its gets cold enough for the heat strips to come on is the heat pump unit outside suppose to be running? i was told it is not suppose to be running they said it would create a double electric bill which i have thank you. i was told only the fan upstairs is suppose to be running to push the heat strip heat out.
    summer1961 says he was told the above,My guess would be that was by his or her Pro,and it's wrong.

    If the heatpumps not running and the strip heat is,your bill will be much higher ,and in some cases double.

  12. #12
    Join Date
    Jan 2005
    Posts
    17
    Post Likes
    Thread Starter
    thank you to all who replied back.jus trying to get a another opinion because this is a new heat pump and is very cold in this house and the trane installer for our new house says nothing is wrong. thank you again

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,868
    Post Likes
    An under charge or over charge can cuse the strips to come on to often, and too long.

    Have it checked again.

    Also, what temp are you maintaining idoors, and what have the ouotdoor temps been.

    What seer/hspf is your heat pump.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.