I had a call on a Carrier furnace 58SE175-3. How do I tell if the flame sensor is bad? I can't recall how to set my multimeter to test it. The problem is the over temp is shutting burners down before blower comes on. Any ideas?
-
01-28-2005, 09:37 PM #2
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,980
I never check the flame signal on one of those. You need to look real close at the dimples. Look for rusted lines around them.
I'd guess just put the flame sensor in series with your meter.
-
01-28-2005, 09:46 PM #3
Regular Guest
- Join Date
- Apr 2004
- Location
- Niantic, Illinois
- Posts
- 545
Yes, you put your meter in series between the flame senser and the wire that attaches to the flame senser. Set your meter for microamps and fire unit.
-
01-28-2005, 09:49 PM #4
Regular Guest
- Join Date
- Jan 2005
- Posts
- 38
I had...
...a problem like that before and found the vent cap collapsed where a roofer tried to use it for a stool
-
01-28-2005, 10:58 PM #5
Professional Member
- Join Date
- Jan 2005
- Location
- Central Fl
- Posts
- 49
I'm not positive if that particular model is sensing flame by rectification (single wire going to little bar in the flame), but from what I've read so far, it seems it probably does.
To test, you set your multimeter to microamps DC. Your meter has to be in series with the flame sensor. You will usually read anywhere between 2-8 uADC on your meter when the flame is enveloping the rod. Most controls need to see between .5-1 uADC for flame sensing.
In other words, the control board is looking for the amperage, or flow of current, to sense a flame. This is completely different than a thermocouple which does actually generate millivoltage to hold a magnet in place to keep the gas valve open.
By the way, as the flame sensor gets "dirty", the microamperage will decrease. A brand new furnace will usually, in my experience, generate 5-7 uADC. When you see it dropping dangerously close to the 1 uADC minimum, you might want to try clean the rod.
[Edited by gatorguy on 01-29-2005 at 12:45 AM]
-
01-29-2005, 12:41 AM #6
Professional Member
- Join Date
- Feb 2004
- Posts
- 2,403
uA not MA is microamps I sure you already new that.
-
01-29-2005, 12:46 AM #7
Professional Member
- Join Date
- Jan 2005
- Location
- Central Fl
- Posts
- 49
Good Call. Must have been a Friday night after a 65 hour week when I was typing that
I corrected my mistake. Thanks.
-
01-29-2005, 08:04 PM #8
Professional Member
- Join Date
- Nov 2001
- Location
- Moose Jaw, Saskatchewan, Canada Occupation:Interprovincial Plumber, Commercial Gasfitter Interests:
- Posts
- 2,374
What does a high limit problem have to do with flame signal?????????????????
I love my job, but paydays Thursday
-
01-29-2005, 08:15 PM #9
Professional Member
- Join Date
- Jul 2004
- Location
- midwest
- Posts
- 2,868
I was thinking the same thing but im not a Carrier guy so I kept quiet.Originally posted by rich pickering
What does a high limit problem have to do with flame signal?????????????????
-
01-29-2005, 09:12 PM #10
Professional Member
- Join Date
- Jan 2005
- Posts
- 56
Sorry, the flame sensor was just a question. The high limit was the problem. It kind of ran together!! It's been a bad week.
-
01-29-2005, 09:33 PM #11
Re: I had...
That would trip the high limit on the flue draft. Are you in KC?Originally posted by airmechanix
...a problem like that before and found the vent cap collapsed where a roofer tried to use it for a stool
-
01-29-2005, 10:59 PM #12
Regular Guest
- Join Date
- Nov 2003
- Location
- carpentersville IL
- Posts
- 24
I'm not sure what type of furnace this is either but to start, if it is a counterflow, make sure your filters are clean. Not enough return air and your limit will trip. Circuit board could be malfunctioning and not starting fan in time. If there is no circuit board whatever controls the fan may not be working properly. Thermostat heat anticipator fried or set wrong, limit switch malfunctioning. Check temp at limit when it shuts down. Good luck
-
01-30-2005, 11:31 AM #13
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,980
Isn't that a old green monster with a damper in the flue?
I think they had a cam stat style of limit and a G60 control on the gas valve or mounted above the burners.
When I suspected a flame signal problem I would just clean the flame sensor and fire it up.
If the limit is triping you might try to stick a probe in place of the limit and see how hot it's getting. Could be a bad camstat. I rember replacing more that I thought I should have the last couple of years I work for that Carrier dealer. Seemed like poor quality.
Those furnaces had a coating in the HX. Look close for any rust lines. They could be cracks. Look hard at the dimples and water test if possible.