  1. #1
    the heat strips or aux seldom come on and yes it was warm and sunny in the 40's when it was checked out.when the aux heat does come on the heatpump is on.yes i have a fan pointing upward but does not make a difference.

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,876
    I meant a ceiling fan blow the hot air down from the cathedral .
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    the ceiling fan is in the cathedral ceiling and i have tried it in both directions and it just gets the cold air blowing around more.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,876
    Have them check it again when the temps are coller, and ask them if your t stat has an adjustable heat anticipator, or cycles per hour for second stage.

    If it does, they can set it so the second stage runs longer.
    Also, ask if they can change the balance point stting for your strip heaters if it has a bp setting.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?