Thread: Rheem heat pump problem

  1. #1
    Join Date
    Mar 2004
    Posts
    4
    Post Likes
    I have a 4 ton Rheem heat pump that I'm looking at for a friend. It cools good, and it heats good. The complaint is that he has to reset the high pressure switch on very cold days.

    I slap the gauges on it in cooling and get 40 suction & 150 head on a 75* day. Evap is clean, blower etc. . I tried to add a little gas , no pressure changes...So I tried it in heating mode. Switched my gauges ,fired it up and now really scratching my head ,120 suction ,125 head.

    In cooling mode the center tube on reversing valve back to compressor was cool and right tube was cool . Only 4* temp difference. In heating mode the same two tubes were warm. That don't seem right to me? Should it be the tube on left now for heat. RLA for comp 29.1 It was pulling 14.3 in both modes. Is my RV bad ? Or is this scroll compressor kicking my butt ? Also flutter on high side gauge in heat mode only. Heat pumps a rare for me to see.

  2. #2
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    Originally posted by searstech3
    Rheem heat pump It cools good, and it heats good.
    The high pressure switch opens at 450psig,I think.
    maybe bad switch, (or blocked meterdevice,kinked line....)

    Sounds undercharged,but cant know without a suction line temp.40 is too low.

    Rev.valve sounds good.

  3. #3
    Join Date
    Jan 2005
    Posts
    17
    Post Likes
    you might check your indoor coil and filters also return sizes these things can cause high pres in the heat cycle as well as if it is an electric airhandler make sure heating element are not all on when in w1 and that there is outdoor stat that cuts hp off below 30 degrees when aux is called for only 1 or 2 heating elements should be on if it is a duel fuel system that is a whole different ball game

  4. #4
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    ....or a mis-matched coil and heatpump....

  5. #5
    Join Date
    Apr 2003
    Location
    Iowa
    Posts
    772
    Post Likes
    do you have enough air flow on inside coil for one thing?

  6. #6
    Join Date
    Aug 2003
    Posts
    82
    Post Likes
    many things to look at first were are gauges connected and what kind of metering device is insde and out side?
    does this system matched?
    post more info?


  7. #7
    Join Date
    Jun 2002
    Location
    Jacksonville, Fl
    Posts
    106
    Post Likes
    The pressures are too low. Also the suction line to the compressor should never be warm. It sounds like the compressor was not running thereby equalizing the high & low pressures & that would also explain why the warm suction line between the reversing valve and the compressor.

  8. #8
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Sounds like a hanging reversing valve to me.

  9. #9
    Join Date
    Jun 2003
    Location
    Hell Hole Swamp
    Posts
    4,255
    Post Likes
    Staying in defrost too long maybe, I cant see a stuck RV or one leaking by causing the HP switch to trip, that would make the head pressure lower and the suction higher, you may have more than one problem

  10. #10
    Join Date
    Dec 2004
    Posts
    201
    Post Likes
    expansion valve in the outdoor unit is bad or the bulb is off not touching pipe. just a guess!

  11. #11
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    Originally posted by searstech3
    the same two tubes were warm.That don't seem right to me?
    No, it aint right.
    Should it be the tube on left now for heat.
    On the side with three lines (bottom) you want the middle and one side or the other to be cool.On the side with one line (top) you want it and one of the bottom lines to be hot.
    Is my RV bad ?

    Something's wrong. Let us know how you solved it.

  12. #12
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Originally posted by swampfox
    Staying in defrost too long maybe, I cant see a stuck RV or one leaking by causing the HP switch to trip, that would make the head pressure lower and the suction higher, you may have more than one problem
    He said that when he switched it to heating his suction was 120 and head 125. Thats high suction and low head, isnt it?

  13. #13
    Join Date
    Feb 2004
    Posts
    2,597
    Post Likes
    make sure your low side is attached to the common suction port.
    put the system into a forced defrost and see what happens to the high side(liquid line). you may have a clogged or immovable accuator.

    good luck

  14. #14
    Join Date
    Mar 2001
    Posts
    19
    Post Likes
    I HAVE RUN INTO THIS PROBLEM MYSELF. I INSTALLED 13 13SEER RHEEM SYSTEMS THIS YEAR. IF YOU DO NOT HAVE AT LEAST 24 INCHES OF STRAIGHT DUCT COMING OUT OF THE AIR HANDLER, IF IT IS A RHEEM AIR HANDLER, IT WILL GO OFF ON HIGH PRESSURE. IT IS NOT GETTING ENOUGH AIR FLOW. THIS CAME FROM THE RHEEM TECH REP IN OUR AREA. THE ONLY THING YOU CAN DO IS BLEED OFF UNTIL YOU GET ABOUT 250PSI ON HIGH SIDE IN THE HEAT MODE. OTHERWISE YOU MUST ADD SUPPLY DUCT AT THE AIR HANDLER. BEEN THERE, DONE IT.

  15. #15
    Join Date
    Feb 2004
    Posts
    2,597
    Post Likes
    you don't really go by a 250 psi for all outdoor temps., do you?

    please, say it aint so.

  16. #16
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    And here I though the installation instructions were just a kneepad full of information just to make an installers life miserable by printing information to make the system run correctly.

  17. #17
    Join Date
    Mar 2001
    Posts
    19
    Post Likes
    IT IS NOT SO. SORRY FOR GIVING THE WRONG INFO. GO BY THE CHARGING CHART ON THE COVER. 250 PSI WAS JUST A REFERANCE POINT.

  18. #18
    Join Date
    Sep 2004
    Posts
    51
    Post Likes
    [QUOTE]Originally posted by searstech3
    I slap the gauges on it in cooling and get 40 suction & 150 head on a 75* day. Evap is clean, blower etc. . I tried to add a little gas , no pressure changes..

    You didn't add enough if the pressures didn't change. Add refrigerant until you see a change.Is the blower running? Post more info if you want help



    .So I tried it in heating mode. Switched my gauges ,fired it up and now really scratching my head ,120 suction ,125 head.

    What guage port are you on? You are on the wrong suction port if your amp draw is the same in both modes.Need more info.

  19. #19
    Join Date
    Oct 2004
    Posts
    209
    Post Likes
    First of all..If you had to switch your gauges between heating/cooling modes then obviously your suction hose was not on the correct suction port. That would be the third port on the machine you didn't see...all rheem heat pumps have it..

    If your head pressure switch is tripping in heating mode... it could be one of the following but not limited to:

    1. bad powerhead on outdoor txv or debris in the outdoor metering device.

    2. defective defrost termination thermostat or defrost control board

    3. dirty indoor coils or indoor airflow problem ie..indoor blower motor not up to speed..(due tothe fact you have a 40# suction in cooling mode)or possibly indoor motor going out on overload in heating mode

    This is where I would start....

    Let us know what happens....

    I hate when someone asks for help and never again replies....


  20. #20
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    I'd skip 1 and 2 until you verified 3. Poor ductwork should be added to it, then, if my airflow was correct, I would verify an equipment match, my line size, length and vertical seperation are within the guidelines in the manual. Then if all that is ok you should pull the refrigerant, tripple evacuate (break with nitrogen) and weigh the charge back in. Then if you still have problems you can begin the parts guessing.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •