Results 1 to 7 of 7
  1. #1
    Join Date
    Nov 2004
    Posts
    5
    My local inspector is doing some code research for me concerning required duct sealing options but since code is the minimum standard, I would like to know the best method(s) to ensure an air tight duct system. For instance, in an extended/graduated plenub comprised of hard round pipe, how should the connections be sealed? What about branch offs of flex? What about insulating options for round pipe? Note: this is a crawlspace installation.

  2. #2
    Join Date
    Feb 2004
    Location
    Knox CO. KY Occupation: Residintial and Commercial instalation, service,and commercial refrigeration. Interests:4wheeling and Hunting
    Posts
    153
    We use hard pipe and we tape each connection with foil tape and insulate everything but the return in a crawlspace, but we do tape all connections of the return and we also use duct sealer on the return. It works great with no duct leakage we have done a blower door test on a couple of jobs and have to shut it down pretty quick.

  3. #3
    Join Date
    Jul 2003
    Location
    sacratomato
    Posts
    535
    Anything you use needs to be UL-181 approved. A lot of people use mastic duct sealant, it’s a white water based compound you apply with a short bristle brush. There is a foil tape with a butyl rubber on one side. (foilgrip 1402)Carlisle makes both products.
    http://www.hardcast.com/PRODUCTS/pr_detail.asp?pid=3

  4. #4
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    6,175
    Bldg. scientist recognize only duct sealing mastic. Tapes often don't stick to the oily metal or the fall off as the acrylic adhesive breaks down over time. Go to http://www.infiltec.com and read about duct sealing in the links section.
    HTH

  5. #5
    Join Date
    Feb 2004
    Location
    chicago suburbs
    Posts
    4,422
    FILL OUT YOUR PROFILE!!

  6. #6
    Join Date
    Nov 2004
    Posts
    5
    I appreciate the responses. Sounds like foil tape ( the mastic type ) is acceptable. My contractor actually brushes mastic over the foil tape, though it got overlooked on my job. However, when I inquired about what was proper, he insisted on going back and putting mastic over all the foil taped joints. He says thats how they normally do it and his mechanic just dropped the ball.

  7. #7
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    better jobs have insulated & sealed crawls -- read threads here & info @ BUILDINGSCIENCE.com -- then do not insulate ducts in crawl, nor floors above.

    mastic sealing all seams, joints, cracks of ducts & plennums is good -- [ although my 1974 duct tape is excellent -- ALL still sticks tight to GI round!! ]

    mastic over the foil tape is wasteful -- use a better foil tape, or just the mastic, IMHO.

    BTW, I even put mastic at the metal edges of my panned return -- ok after 2+y.

    [Edited by cem-bsee on 02-02-2005 at 09:48 AM]

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  